Hi all,
I have a Nest stat, heatlink mounted and has a 4 way & earth connected with a separate 2 way connected.
2 way to go to wall stat T1 & T2 12v from the heatlink.

Earth to earth
Heatlink L to L on boiler
Heatlink N to N on boiler

Question is 2 & 3 on heatlink ( i think are supposed to go to TA TA ) on boiler can someone confirm and can they go either way round.

Currently the TA TA go to the old wall Stat (still connected until I'm sure which way round it needs to go)

Cheers guys
 
If the two TA terminals current have the thermostat connected between them then yes you would remove the existing connections and connect the nest terminals 2 and 3 to them. It's just a switch so it doesn't matter which way round they are.
 
Thanks for the quick reply, to confirm I have realised it's not both TA connections it is the Top one which is = and the next one down which is TA.
Attached are 3 photos
1. Nest diagram 2 & 3 used.
2. Vokera terminal block diagram.
3. Actual photo of current active connections.

I'm presuming it's still the same no 2 and 3 from heatlink to the = and 1st TA terminal to replace the 2 that I will take out.

Cheers all.
[automerge]1586186572[/automerge]
Forgot to add attachments.
 

Attachments

  • Screenshot_20200406-154736_Drive.jpg
    112.4 KB · Views: 6
  • Screenshot_20200331-153743_Messenger.jpg
    68.2 KB · Views: 6
  • 20200406_162206.jpg
    75.7 KB · Views: 3
Last edited:

Reply to Vokera linea 24 Nest install in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
I have pulled out an old evaporative system I purchased many years ago from storage to have a look at it and see if I can get it running. Was...
Replies
1
Views
191
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock