I have tested the neutral to earth from the mains to my main panel and it is reading 4 meg ohm.

Neutral to earth resistance at the main incoming is reading 0.

But voltages are all ok and equal
 
Have you verified the neutral St the distribution board.

Is anything else in the building suffering from a potentially floating neutral.
I have had uk power networks out and they have checked their supply and all is fine. I can only seem to find this fault on these contactors because they are the only ones which have a neutral in the system for the pilot light. The main lighting and single phase sockets in the building have 242volts but obviously cannot test anything once load has been removed like I can on the three phase circuits.
 
So what does the customer make of this

2 days in, a call out from the DNO and still no solution.

You say that the neutral is only at the contactor for a pilot light.

What goes to A2?
He is worried about this voltage.

Basically this is what I have found so far.

First conveyor DOL starter is wired as normal. 3phase 415 coil fed through overload etc.

Control wire for second DOL starter comes out of T2 of first conveyor to a proximity sensor (to shut off motors when bin is full)in the storage tank which is through n/c contacts on a relay to enable a siren to be muted when bin is full then back to NO contact number 13 on 2nd starter.

What I'm finding is when the first contactor is turned off the second remains pulled in and the voltage at number13 of the no contact on the contactor is 560v to earth.

If I disconnect the neutral from the pilot light in the control box which tells the operator it's going to the bin (also fed from l3 on the first starter) it all shuts off and the interlock works fine and no excessive voltages.

My question is now this. Am I trying too hard yo find the neutral as the fault when it could be something more simple like in the relay and back feeding down the neutral to the contactor as the pilot light obviously more than doubles in brightness when this happens.


And just realised I haven't answered your originsl question

A1 is fed from L1 and A2 Is fed through this control circuit through overload etc from L3.

The neutral for the pilot light is taken from the consumer unit which supplies these starters.
 
Hi,i think you may need to do some alternative tests,using the appropriate equipment,for those tests.
Some of the results,you already have,may be leading you to the wrong conclusion.

Accepting the test gear you are using,and discounting any alternative supply to the building,generator supply,PV,etc have you done a full set of voltage tests,at the supply,when the machine is set-up to give that 550V reading in your picture?
 
Last edited:
Hi

I have been called out to a fault on a grain dryer where the motor interlocks are not disconnecting. Previous conveyors. Upon investigation I have found one starter that does not disconnect the preceding motor but when tripped I am getting 550v to earth from a1 and wait for it 760volts to phase from a1! This has baffled me as there's only 410v incoming.

Thoughts?
Is your plant a 3 phase ungrounded delta or is it a 4 wire y connection and is the line voltage 600 or 480
 
Is your plant a 3 phase ungrounded delta or is it a 4 wire y connection and is the line voltage 600 or 480

We're in the UK, our voltages are different, and we don't use delta supplies. Our normal service except for new, very large installations is 230/400V 4-wire Y. So anything over about 430V is abnormal.

Let's look at the possibilities.

1) The high voltage does not exist. The voltages being shown are not the actual voltage present, due to interference from a VFD or similar, causing the instruments to malfunction.

2) The voltage actually exists, and is coming from the supply. This doesn't make sense. If you lose the neutral on a 230/400V supply, 230V single-phase circuits can receive anywhere between 0 and 400V. 3-phase circuits will still have 400V between each phase and another, but the neutral could be anywhere from 0 to 400V from each of them. Nowhere does the voltage rise above 400V.

3) The voltage is being produced within the panel / system. I don't think it's been explicitly stated what the control voltage of these contactors is. Do some / all of the coils operate at 230 or 400V? If there is a control transformer in the panel, a fault on the secondary that puts it in contact with a line of the primary, could add their voltages. It would be possible to have say 510V from one 110V control wire to one line wire, if the other side of the control supply is in contact with another line. There are some very unlikely scenarios that we could think up, where isolated devices that can behave like transformers could add to make higher voltages still.

But all of this is just conjecture if we can't see the circuit!
 
The
We're in the UK, our voltages are different, and we don't use delta supplies. Our normal service except for new, very large installations is 230/400V 4-wire Y. So anything over about 430V is abnormal.

Let's look at the possibilities.

1) The high voltage does not exist. The voltages being shown are not the actual voltage present, due to interference from a VFD or similar, causing the instruments to malfunction.

2) The voltage actually exists, and is coming from the supply. This doesn't make sense. If you lose the neutral on a 230/400V supply, 230V single-phase circuits can receive anywhere between 0 and 400V. 3-phase circuits will still have 400V between each phase and another, but the neutral could be anywhere from 0 to 400V from each of them. Nowhere does the voltage rise above 400V.

3) The voltage is being produced within the panel / system. I don't think it's been explicitly stated what the control voltage of these contactors is. Do some / all of the coils operate at 230 or 400V? If there is a control transformer in the panel, a fault on the secondary that puts it in contact with a line of the primary, could add their voltages. It would be possible to have say 510V from one 110V control wire to one line wire, if the other side of the control supply is in contact with another line. There are some very unlikely scenarios that we could think up, where isolated devices that can behave like transformers could add to make higher voltages still.

But all of this is just conjecture if we can't see the circuit!
the voltage in the states for a house is normally 120/240. When you lose your neutral the 120 will go up to 190 which will fry clocks, TVs or anything plugged into to the sockets which we call receDo y’all use ground rods to bond your service.
 
Bond
The

the voltage in the states for a house is normally 120/240. When you lose your neutral the 120 will go up to 190 which will fry clocks, TVs or anything plugged into to the sockets which we call receDo y’all use ground rods to bond your service.
Bonding the neutral is the most important thing you can do and we call sockets receptacles in the states
 
So when the contactor is off and the machine is isolated.

What is the continuity between

L1 Common and L1 Load.

L2 Common and L2 Load.

L3 Common and L3 Load.

Also when the coil is de-energising does it completely release, or is it mechanically stuck half way. Does a crack with a screwdriver properly release it?


The 110v is a waste of time. It sounds like you are testing at 2 points on the same phase. Unless the control circuit to pull in the contactor is 110v. I just can't tell from here.

You need to always test the lives with one prong on phase and the other on the earth bar.
Don't do much in the way of Safe isolation then in your place of work?
 
The scribbled wiring diagram is the best I can put together and get photo'd for attachment at this time of the evening. Take a look at it which is my take on what Sparky42 has described as the two contactor and control wiring. All contactor coils are 400V. Both motors are three phase 3 wire and star connected. The first motor to start M1 is controlled DOL by the top contactor C1. The second motor M2 is started DOL when C1 closes. The pilot lamp indicates when the first motor M1 is running.

I reckon you may have welded closed L1 contacts on contactor C1. This means you still have control of M1 but L1 out of C1 remains energised at L1 line voltage when the C1 opens. With L1 at 400V there is a current path through the lower pair of windings of M1 and then through the pilot lamp to N. The lower pair of M1's windings interact with the third vertical winding to create a step-up transformer. The voltage on the L2 out terminal of C1 is thereby raised to a higher potential than L1 - what potential with respect to N (550V)and also L1 (760V) in of C1 depends on the voltage drops across the lower two windings and the pilot lamp, all in series.

Thus there is an energising ac emf derived from L1 now applied to the control circuitry of C2 which causes C2's coil to remain magnetised when the original closing emf derived from L2 out of C2 disappears. It requires a smaller current to keep the contactor closed than it does to close if first of all - you can work out why for yourself. This reasoning explains why removing the N to the pilot lamp or control cabinet caused C2 to open after it has been first closed by C1. And why the pilot lamp lamp burns much brighter.

I have faintly shown on the left the way the three windings of M1 act as a step up auto-transformer.

Or something like this explanation..

So, I would check contactor C1 thoroughly and I reckon you will find L1's contacts are welded closed or there is significant tracking happening even when its contacts are open.
 

Attachments

  • 550V.jpg
    1.9 MB · Views: 48
Last edited:
I suspect Marconi may well of hit the nail on the head.

If it not that then I did have similar voltages to earth but across all three phases not between phases though (well higher closer to 620v) a few years back. In a factory with a guaranteed(ish) supply. It had two independent HV supplies that would switch automatically to the back up if the normal supply failed. They were supposedly interlocked on both HV and LV sides of the sub station.

At the time the fault presented itself, both HV circuit breakers were closed therefore both transformers were live. The LV side was still open on the second supply but because of the interaction between the earthing and neutral it gave strange readings between Live and earth. An analogue meter would jump up then slowly drop back to virtually nothing. It disappeared after the HV breaker was opened. Not by me I will add !
 

Reply to Volt meter reading 760volts in 3phase dol starter overloads in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Advise Please. Called out to my local farm, who deal in fruit and veg, to a DOL starter switch which cuts out after a minute or so. This switch...
Replies
28
Views
8K
I'm going to be learning to interlock conveyors so that one cant start without the preceding one running. For safety purposes. I'm working with a...
Replies
5
Views
2K
I've recently purchased 4 Helios 275 watt solar panels. My plan is to run a 48 volt system. 2 panels will be in series and both sets of 2 panels...
Replies
1
Views
1K
H
Anyone tell me what Ive done wrong here lads? Wired up a starter today, 2 DOL contactors with 415V coils fed through two Telemec Motor Overload...
Replies
34
Views
8K
B
Hi all Any industrial electricians in the house ? Having decided to move my old Harrison L5 lathe to a more suitable location in my workshop...
Replies
14
Views
31K
Knobhead
K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock