I get this with all ends of the circuit disconnected from MCB and bars.. Seems to be an interconnection somewhere to the circuit... Currently doing more test
Look for faults local to the CU as the circuits will separate soon after.
From the readings this could be a floating voltage, but could also mean that the earth to your circuit is connected to line. However if the cables are all disconnected there is no reference for the voltage to be measured against.
I had a similar experience with my Metrel MI3125B and following a conversation with Metrel Support (01924 245 000) I sent the tester off for repair. I also noted that the measurements remained even with the neutral lead disconnected.
I also had very different readings from my multimeter.
Going to have to start splitting the ring down, going to be a nightmare to find.. I just can't think of where this link could be between the two circuits. The nearest accessory to the 3rd floor RFC is the light fitting on 2nd floor landing area..
Logically that location sounds correct, if the ground floor lights are one circuit and this circuit includes the stairwell / landing lighting then the fitting for the landing light would be in the ceiling where the socket circuit is located in the floor above, so that would be a good place to start. Lovely lofts!