A
acvc
Hello folks.
**** PLEASE NOTE: I AM A FIVE WEEK WONDER. If you don't like me, please don't have a go as it's getting really really tedious, unless I appear dangerous to the public or myself.... ****
I have read a lot of posts regarding the need/not need for ME bonding of services.
I've got a bungalow job where the water incomer is plastic. It enters under the kitchen sink where there's the stopcock and it's copper to the taps, and then goes off in plastic.
InsRes reading at 250V between taps and MET is 67.2ohms. I'm going to 10mm bond it.
InsRes reading at 250V at bathroom bath taps is 0.00ohms. I can't get under the bath or bathroom sink to identify plastic or copper, which doesn't really matter given the readings.
There's an electric bathchair type of thing fitted to the bath for the disabled lady who lives there. Are these kinds of disability equipment ever earthed to the bath and therefore introducing a parallel earth path back to the MET? Even if it does I wouldn't expect a reading of 0.00ohms.
I've read Richard Burns' recommendation of removing the main earth when doing the InsRes (>22kOhm) test and will try this when I return.
0.00ohms suggests to me that there is already bonding in place but there's none at the CU.
(It's PME, 30mA RCD protected).
There are two schools of thought on this. The 'bond everything' vs the 'test to identify ExtrCondParts' schools.
Short of ripping this lady's bungalow apart to bond across the breaks in the copper piping, I assume that I'd have to bond run separate 10mms to each ExtrCondPart found, testing back to the MET as I go so I know when to stop.
Anyway, sorry for the rambling mess of a post.
Any thoughts gratefully received.
My read is, if any metalwork that you may think needs supplementary bonding, the IR between a known earth needs to be more than 0.02Mohms anything less bond it
Thanks Pete999. The circuits in the bathroom are all 30mA RCD protected, and disco times are good so no need for supp bonding, and obviously there's a proven continuity between the ExtrCondParts and the cu MET!
It's the main equipotential bonding that's the query.
I would bond the gas and water as near as possible to the entry point of both gas and water and note this on your installation certificate, others may pooh pooh that idea but thats what I would do
You asked not to have a go at you - fair enough.
However, you then go on to state that resistance between taps and MET is 67.2 ohms when it is obvious to us (but maybe not someone else reading it) that this is actually 67.2 MEGAohms.
This is quite a significant difference (in fact a million times difference) and has a significant effect on the resulting actions.
Then a result of 0.00ohms when meaning 0.00 MEGAohms.
This reading actually could be anything below 500,000 ohms so you need to determine what it actually is.
Thanks Geoffsd.
What I didn't say, was that I firstly got a reading of 0.00Mohms between kitchen taps and MET. Thinking that my meter would not be hugely accurate at low resistance readings from InsRes testing, I did a continuity test which was what provided the 67.2ohm reading.
Apologies for not being clearer on this.
Hello folks.
Short of ripping this lady's bungalow apart to bond across the breaks in the copper piping, I assume that I'd have to bond run separate 10mms to each ExtrCondPart found, testing back to the MET as I go so I know when to stop.NO!....The only concern with main bonding is on incoming extraneous conductive parts. Bond at the point entry or near as practical and it is dealt with. What happens to the pipework beyond that point is irrelevant,as within the fabric of the building it can no longer pick up an external earth potential.
Thanks for that wirepuller.
So even if the main bonding is in place at where the water enters the dwelling, and - after the plastic piping in the dwelling - there are still ExtCondParts as identified by the 23kOhms test, then there is no requirement to bond these?
Many thanks.
Many thanks.
Main bond incoming services at the point of entry if they are extraneous. Beyond that only special locations such as bath/shower rooms need to be considered for supplementary bonding.
Remember,main bonding an incoming service is to deal with a hazard from outside the property,once bonded at the point of entry it's dealt with.
Thanks again. That makes good sense.
The electric bath chair thing was getting to me, but yes it's RCD additional protected, as are the other ccts in the bathroom.
OK I'll shut up now. Sorry for what seems in retrospect like a daft question.:wacko:
Remember that with an immersion heater, gas boiler and a few other items of equipment, you'll have a cpc connected to the pipework, which will confuse the issue if you're trying to determine whether extraneous or not.
Hello folks.
whats this?