The 40.5V DC that you measured might not be strictly accurate because of the waveform. The rectifier output voltage is DC pulsating at 100Hz, however the current through the magnet is probably fairly smooth DC because of its inductance. When the voltage from the transformer secondary drops too zero on each half-cycle of the AC waveform, the magnet current continues 'flywheeling' through the rectifier.

Selenium rectifiers drop approximately 1-2V per plate under load. Unlike silicon diodes where a single diode junction can be made to withstand >1000V in reverse, each selenium junction can only withstand a few tens of volts. To make a rectifier with higher PIV, multiple plates must be stacked in series, each adding to the voltage drop. Your rectifier appears to have two plates per diode, therefore as two diodes are always in series with the load, a forward drop of 4-6V would be reasonable. Note that there is an extra diode at the bottom not in use.
 
So i need to check the electric motor now if it's possible to make it run under single phase or i have to change it with a new one. I will also need to change the transformer with another one for 230/45v.
If i use the same rectifier will that be a problem?
 
Transformer will be a straight swap you just need the correct va, rectification can be left in place.
 
Output is 2×24v and you can normally connect for 24v parallel or 48v series.
 
Indeed, and with a +15V tap on the primary, you connect the 245V primary to 230V and the 24+24V secondaries in series give you 45V as per the existing one.
 