cliffed

-
Arms
Supporter
Reaction score
645
Just improved the mains set up @ local unit basically took out Henley blocks & reconnected into new smallest busbar unit.
This supplies 5 TPN DB & usual tests @ those DB’s will be done for the sub main supplies only.
Certification will be given for the above, will a Minor Works be ok.
 
In my opinion I’d have to err on saying no as MWC is really for changes/additions to final circuits not changing the supply characteristics for 5 consumer units. I’d love to be proved wrong though.
It’s a pain sometimes, a frequent similar irritation for me is swapping an MCB for an RCBO needing an EIC.

In this case I’d probably treat the bus chamber as a consumer unit and list the five ‘circuits’ and the test results on an EIC making it very clear what the scope is.
 
In my opinion I’d have to err on saying no as MWC is really for changes/additions to final circuits not changing the supply characteristics for 5 consumer units. I’d love to be proved wrong though.
It’s a pain sometimes, a frequent similar irritation for me is swapping an MCB for an RCBO needing an EIC.

In this case I’d probably treat the bus chamber as a consumer unit and list the five ‘circuits’ and the test results on an EIC making it very clear what the scope is.
Cheers a EIC it is
 

Reply to What cert for busbar chamber in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Not come across this before, so would like some help, please. I went to install smokes and heat alarm (to new Scottish regs) in a fairly modern...
Replies
2
Views
1K
Basic question to see if what I wish to do is correct: Client wants to build (or is building) and outside room (roughly 8m by 4m) to be used as a...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock