What do I think?
Well at first glance the testing looks plausible, missing R2 for some circuits but apparently Zs has been done for all.
Ze is 0.11 ohms. But lighting Zs results look low, especially upstairs lighting.

If it's a split load board, the wiring is probably pre 2004, so IR tests are believable, it might be the software that wants ranges not exact values.
On the other hand, I'm confused by the inspection schedule, as clearly all circuits in bathroom don't have RCD protection. So I'm not sure I trust the rest of it.

Presumably you've seen the actual installation, what do you think?
 
Its the RCD bit that confused me .Thats why i am throwing it out for opinions !
I’d imagine that they’ve just recorded the X5 value and only recorded the result in the RCD box, then not bothered to follow it on down the column.

Maybe from software that auto records results from meter as you test?
 
Its the RCD bit that confused me .Thats why i am throwing it out for opinions !
It would help to to see the previous pages.
You'd expect to see 6.1 ticked, or 6.4 ticked, or codes. As it stands it doesn't make sense and without more of the report I can't say whether this is a single oversight or indicative of the rest of it.
 
Only seeing four pages of the EICR makes it difficult to fully assess it as there is no indication of the age of the installation
As has previously been mentioned it looks like a prefilled cert that has had little or no editing and has not been proof read before being handed to the client
 
Looks to me like they used a "tick all" button....and didn't undo the ones that make no sense, like the famous RCD for fault protection.

I always look for that as well as it shows a general lack of understanding..

I hate these automatically generated rubbish EICR's as with their yes to all shortcuts and autofill etc but actually can't see too much wrong with this EICR, I think with the price pressure on an EICR you cant spend 3hrs making sure all of the paperwork is 100% correct however much you would want to.
 
Well, we only know what we know!
If you take the test results page at face value, then we have an installation which meets requirements for ADS, additional protection is present and working (except lighting circuits) and the wiring itself is in reasonable health.
We don't know (off top of head)
-size and condition of tails, condition of cut-out
-details of supplier fuse
-size of main earthing
-earthing type (though can guess TNCS from the PFC given)
-presence of bonding
-whether the special location is actually ok

If all the above is all ok and there is supplementary bonding in the bathroom then it might indeed all be "Satisfactory".

When I explain EICR certificates to people I say that the last page of test results is more "showing your working" and the important bit is the schedule of inspection. But in this case there isn't really one, it's all "ok", even things that don't exist or are not accurate.
So inconclusive really.

I'm curious @LukeD what your involvement is - are you there for more work, or do you know the owner?
 
I always look for that as well as it shows a general lack of understanding..

I hate these automatically generated rubbish EICR's as with their yes to all shortcuts and autofill etc but actually can't see too much wrong with this EICR, I think with the price pressure on an EICR you cant spend 3hrs making sure all of the paperwork is 100% correct however much you would want to.
In my view the entire model form should be revised to have a customer-friendly half that they have a hope of understanding.
 