Discuss what is the best thing to do here in the UK Electrical Forum area at ElectriciansForums.net

N

NadHuh

Someone's already wired this but I am not sure what he was going to do if you have a look at this http://sli.so/9319603NQ
It looks like it is a ring so what is the best thing I can do I was thinking of adding another socket and crimping one cable with one leg behind the
socket and the others cable with the others leg connected to a socket is this the best solution?
 
I will open a whole can of arguments here but solid drawn cables shouldn't be crimped, the crimps are not designed for solid and although it may seem tight the ratchet can crush the solid cable, miscrimp and the joint is usually highly suseptable to failure especially if moved about in it lifetime as it easily loosens.
In line cable splices are designed and can be used on both stranded and solid cables, the amount of failed crimps on solid ive come across is unbelievable.
There are others on this forum that say they never had problems but if you talk to the manufacturers about it they generally recommend you dont use on solid drawn cables, stranded cables can adjust to the shaping of the crimping action giving a good tight crimp, when solid is used the butt crimp can deform and/or the cable can be crushed and weakened and on top of this as already noted the joint may seem tight but is easy to wiggle loose.
 
I will open a whole can of arguments here but solid drawn cables shouldn't be crimped, the crimps are not designed for solid and although it may seem tight the ratchet can crush the solid cable, miscrimp and the joint is usually highly suseptable to failure especially if moved about in it lifetime as it easily loosens.
In line cable splices are designed and can be used on both stranded and solid cables, the amount of failed crimps on solid ive come across is unbelievable.
There are others on this forum that say they never had problems but if you talk to the manufacturers about it they generally recommend you dont use on solid drawn cables, stranded cables can adjust to the shaping of the crimping action giving a good tight crimp, when solid is used the butt crimp can deform and/or the cable can be crushed and weakened and on top of this as already noted the joint may seem tight but is easy to wiggle loose.
well...i`ll be honest here and say i`v had to crimp solid cable in the past....and yep...i identify with what your sayin dark....as i`v had em pull out from time to time....so i allways tug em first...just to be sure.....
but a bit of due care n attention whilst crimping usually gets em...
 
I always thought that crimping solid core was more reliable than crimping multi...

Decent crimping tool and you'll deform the core so the crimp won't come off...

Personally I crimp both and do a tug test. Had failures occasionally with both solid and multi, but usually fine.
 
I will honestly confess i have done before myself before i learnt about the pitfalls, and agree the crimp can seem deceptively good but rather than tugging it try wiggle it left and right and see how quickly it fails, stranded dosn't have this issue because the strands take up all the movement away from the crimp and also they give a reliable crimp to start with.

In cases where the cable never moves your can usually get away with it this is why it can seem 'deceptively' an OK method but you shouldn't apply that reasoning as an argument to use this method especially when alternatives exist.
One accepted method is uninsulated crimp then soldered with heat shrink to finish but space restrictions do limit this method and its time consuming too.

Personally i never entertain the method of crimping solids in thi fashion anymore and will go the extra step in a job to find an alternative solution.
A peak into industries that use plenty of crimping in cables will re-inforce this as they all ban crimps of this nature been used on solid, i.e. Railtrack, NASA, Aviation etc etc and understandably as the consequences are alot higher than a domestic fire.
 
I will honestly confess i have done before myself before i learnt about the pitfalls, and agree the crimp can seem deceptively good but rather than tugging it try wiggle it left and right and see how quickly it fails, stranded dosn't have this issue because the strands take up all the movement away from the crimp and also they give a reliable crimp to start with.

In cases where the cable never moves your can usually get away with it this is why it can seem 'deceptively' an OK method but you shouldn't apply that reasoning as an argument to use this method especially when alternatives exist.
One accepted method is uninsulated crimp then soldered with heat shrink to finish but space restrictions do limit this method and its time consuming too.

Personally i never entertain the method of crimping solids in thi fashion anymore and will go the extra step in a job to find an alternative solution.
A peak into industries that use plenty of crimping in cables will re-inforce this as they all ban crimps of this nature been used on solid, i.e. Railtrack, NASA, Aviation etc etc and understandably as the consequences are alot higher than a domestic fire.
hmm....consequences of the loss of a single life due to my actions ....would drive me to voulenterally hang up my test leads for good dark....
 
i'm with darkwood on this. had no end of failures when crimping solid. crimped it, tugged it, fell apart, cut , new crimp, try again. get a better joint with yellow crimps on 2.5mm with the cores overlapping, not butted. even the dreaded choc blocks are more reliable. i blame the metricate everything brigade. was no problems with 7/029. and you could bend it when cold.
 

Reply to what is the best thing to do here in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
309
Not sure what to do here. I am wiring detectors for someone, boiler is in a small cupboard in the bathroom. Too small to fit the detector as it...
Replies
5
Views
255
I was asked to see why a set of sockets weren’t working in the house (which appear to be a ring circuit based on breakers) There was no power on...
Replies
27
Views
1K
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
343

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock