@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:

643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement

GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
 
Reading that 643.3.1, the wording of "live" conductors suggests live, as in energised.
IR is a dead test.
 
Reading that 643.3.1, the wording of "live" conductors suggests live, as in energised.
IR is a dead test.
It’s referring to the line and neutral conductor, both of which are classed as live conductors. It’s also lumping the 4 live conductors of a 3-phase board together for simplicity (3 line + neutral).
 
@ToonSparky is correct to terminate into the board before testing, at least for the CPCs anyway. If you're not connecting the CPCs to the earthing arrangement, then your IR testing is non compliant:

643.3.1 The insulation resistance shall be measured between live conductors and between live conductors and the protective conductor connected to the earthing arrangement

GN3 (17th ed, am3) tells me that this requirement came in in 2008, prior to this you could just test to the CPC without it terminated. Old habits die hard huh?
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
 
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
Sure, no reason I can think of why you shouldn't do it that way. Much easier to find which conductor belongs to which leg of a ring final for the fig.of 8 tests if you do it before the cables are terminated
 
Sounds like you're brasting.....?....or something?
or he's into bondage. as for questioning, every day i question my sanity. but if i can do that, it's proof that I'm not crazy, so still working. Catch 22.
 
Am I being completely thick , but why? do you need to connect the earths to the earth bar to conduct your initial IR tests

at college we did dead tests prior to connecting circuits to the board
 
Maybe this is why I was taught to do it this way back when I was an apprentice.

So it could be worthwhile carrying out all R1+R2 and end to end tests while disconnected from the board but IR tests onwards cables should be terminated?
This is what I do
 