I'm preparing an electrical drawing to be submitted to my AWJ (Authority with Jurisdiction) which uses NEC 2014 and IRC 2018. (Important because NEC 2018 changed some requirements). My system is 36 panels producing 12.9kW Dc, and 2 Growatt 5000MTLP-US 5kW inverters, with integral Dc disconnects mounted within 10ft of the array to satisfy NEC2014. They produce 21A max continuous output at 240vac 1phase each, with an internal 26A overload protection device. My First question regards the AC disconnect: What's the requirements of it?

I would like to use a 30A non-fusible 2 pole disconnect on each, specifically the Square D QO200TRNM, spec sheet attached, because its small and inexpensive. But I'm not sure if it has to be pad lockable in the off position, or if it has to be fusible?
 

Attachments

I'm preparing an electrical drawing to be submitted to my AWJ (Authority with Jurisdiction) which uses NEC 2014 and IRC 2018. (Important because NEC 2018 changed some requirements). My system is 36 panels producing 12.9kW Dc, and 2 Growatt 5000MTLP-US 5kW inverters, with integral Dc disconnects mounted within 10ft of the array to satisfy NEC2014. They produce 21A max continuous output at 240vac 1phase each, with an internal 26A overload protection device. My First question regards the AC disconnect: What's the requirements of it?

I would like to use a 30A non-fusible 2 pole disconnect on each, specifically the Square D QO200TRNM, spec sheet attached, because its small and inexpensive. But I'm not sure if it has to be pad lockable in the off position, or if it has to be fusible?
Didn't they explain this on your Solar course Repman?
 
Phillip, That makes total sense, similar to the OSHA lockout tagout requirement for industrial applications in the US. Thank you for your response. I didn't realize this forum was primarily UK based until after I joined today, and I know electrical codes vary from country to country. Even within the US with AWJ applying different versions of the NEC code makes it less about what is logical, and more about what is the applicable code. I was hoping someone from the US familiar with NEC2014 as it's applied to solar could answer. Thanks again.
 
I'm preparing an electrical drawing to be submitted to my AWJ (Authority with Jurisdiction) which uses NEC 2014 and IRC 2018. (Important because NEC 2018 changed some requirements). My system is 36 panels producing 12.9kW Dc, and 2 Growatt 5000MTLP-US 5kW inverters, with integral Dc disconnects mounted within 10ft of the array to satisfy NEC2014. They produce 21A max continuous output at 240vac 1phase each, with an internal 26A overload protection device. My First question regards the AC disconnect: What's the requirements of it?

I would like to use a 30A non-fusible 2 pole disconnect on each, specifically the Square D QO200TRNM, spec sheet attached, because its small and inexpensive. But I'm not sure if it has to be pad lockable in the off position, or if it has to be fusible?
Yes the switch cans be non fusible and it has to be lockable which most of them are
 
Pete999: No, I've never taken a course in Solar. Are you familiar with NEC2014?
I have a copy given to me by a friend, but not really conversant with it, not yet anyway
[automerge]1600754810[/automerge]
Yes the switch cans be non fusible and it has to be lockable which most of them are
Every day a School day
 
Megawatt: Thank you for your response. I hope you are enjoying your retirement, I am, but was looking forward to doing more traveling. Because of Covid, I had to put that on hold and took on this solar project since I now have the time. I've had lots of exposure to industrial controls and machine guarding but none in the residential market. I'm in the permitting stage of the project and need to submit a one line diagram of the grid tied system to the AWJ. I think I can navigate the regulations with a little advise, and will hire a Master electrician to do the electrical installation. I noticed from your bio you've also been on the industrial side of the industry. Have you done many solar installations? Thanks again for your help.
 
Megawatt: Thank you for your response. I hope you are enjoying your retirement, I am, but was looking forward to doing more traveling. Because of Covid, I had to put that on hold and took on this solar project since I now have the time. I've had lots of exposure to industrial controls and machine guarding but none in the residential market. I'm in the permitting stage of the project and need to submit a one line diagram of the grid tied system to the AWJ. I think I can navigate the regulations with a little advise, and will hire a Master electrician to do the electrical installation. I noticed from your bio you've also been on the industrial side of the industry. Have you done many solar installations? Thanks again for your help.
No sorry but I was a controls electrician and always worked in chemical plant, paper plants, oil refineries etc. I’m just started doing domestic last year. I would love to start working on solar panels and doing the install. It’s interesting and that’s the way this world is heading
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Flower Mound, Texas
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Manufacturer / Distributor / Supplier / Inventor - etc
Business Name
Retired

Thread Information

Title
What type of AC disconnect switch is required?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Repman,
Last reply from
Megawatt,
Replies
8
Views
1,547

Advert

Back
Top