Hello All, First of all i am not an Electrician just a DIY enthusiast.
I have just built a garden bar shed and have the following in place. Please see images.
Consumer box in the garage fed by the main house supply. Pic shed 5 and shed 6
shed 5.jpg

this then exits the garage by a fused switch
shed 4.jpg

shed 3.jpg

This feed then enters the bar shed and terminates
shed 1.jpg

My question is that i am NOT going to attempt to do this myself, All i want to do is advice on what consumer unit i need to buy so that i can keep costs down. The bar shed will have 6 double sockets and 1 single socket and a light socket, which i intend to have fitted by round conduit.
Any advice greatly accepted.
 

Attachments

  • shed 5.jpg
    shed 5.jpg
    75 KB · Views: 54
  • shed 6.jpg
    shed 6.jpg
    91.4 KB · Views: 62
Hello All, First of all i am not an Electrician just a DIY enthusiast.
I have just built a garden bar shed and have the following in place. Please see images.
Consumer box in the garage fed by the main house supply. Pic shed 5 and shed 6
View attachment 59116
this then exits the garage by a fused switch
View attachment 59117
View attachment 59118
This feed then enters the bar shed and terminates
View attachment 59119
My question is that i am NOT going to attempt to do this myself, All i want to do is advice on what consumer unit i need to buy so that i can keep costs down. The bar shed will have 6 double sockets and 1 single socket and a light socket, which i intend to have fitted by round conduit.
Any advice greatly accepted.
By the looks of the spur in the garage,the most power available in the bar would be 13amps,so any mcbs in the in the shed may be overridden if they are bigger than 10 or 6 amp.So maybe a 10A for sockets and 6A for lighting in a 2 way cu.Hope the cable to the shed is suitable.
Regards,S
 
If it's already fused down to 13A then to save money your electrician could just use a switched fused connection unit at 3A for the lighting.

If it is fused you will have all 6 sockets on a 13A fuse so loading could be an issue depending on what you have plugged in.
 
this job needs a bit of a rethink. first you have a RCD in the garage CU, so another one in the shed would lead to problems with discrimination. i.e. a fault in the shed could trip either RCD. and if the whole lot is fed from an RCD protected way in the house, more trouble.
 
simplest way (and cheapest) is as ferg says, wire direct to sockets and fit a FCU (5A) for lights. bear in mind that your max. amperage will be 13A. unless you can replace the 13A FCU in the garage with a 20A MCB in enclosure.
 
if the cable to the shed is 2.5mm, then 20A would be the appropriate fuse/MCB
Hi, The cable running from the fused socket in the garage to the bar shed is the following
Electric Cable BS 5467 600/1000V...looks like it fed from the double socket next to it ...see photos...ignore the smaller cable on the outside pic..that is my extension cable
 

Attachments

  • pic 1.jpg
    pic 1.jpg
    81.7 KB · Views: 57
  • shed 3.jpg
    shed 3.jpg
    176.3 KB · Views: 50
If the armoured cable is 4mm then it could be connected to the socket (assuming the double socket is on a rfc (ring final circuit) protected by a 32A mcb, without any further protective device.
If the double socket is already a 'spur' off the rfc then you need to seek further advice on best way forward.
If only 2.5 sq mm then a protective device will be required (20A mcb!)
RCD protection by one protecting the rfc?
Not sure why there is an IP rated s/fcu in the garage at all?
[automerge]1593463134[/automerge]
Think the armoured cable is 6mm or 8mm
'Thinking' doesn't do it. 8mm is a non standard size so doubt its that.
sq mm refers to the actual cross sectional area of the copper conductor NOT the diameter of the cable/core.
 
Last edited:
If the armoured cable is 4mm then it could be connected to the socket (assuming the double socket is on a rfc (ring final circuit) protected by a 32A mcb, without any further protective device.
If the double socket is already a 'spur' off the rfc then you need to seek further advice on best way forward.
If only 2.5 sq mm then a protective device will be required (20A mcb!)
RCD protection by one protecting the rfc?
Not sure why there is an IP rated s/fcu in the garage at all?
Think the armoured cable is 6mm or 8mm
[automerge]1593463068[/automerge]
If the armoured cable is 4mm then it could be connected to the socket (assuming the double socket is on a rfc (ring final circuit) protected by a 32A mcb, without any further protective device.
If the double socket is already a 'spur' off the rfc then you need to seek further advice on best way forward.
If only 2.5 sq mm then a protective device will be required (20A mcb!)
RCD protection by one protecting the rfc?
Not sure why there is an IP rated s/fcu in the garage at all?
If the armoured cable is 4mm then it could be connected to the socket (assuming the double socket is on a rfc (ring final circuit) protected by a 32A mcb, without any further protective device.
Source URL: What type of consumer box - https://www.electriciansforums.net/threads/what-type-of-consumer-box.187941/ That socket is the last one of the circuit of 4 doubles and is protected by a 32amp mcb
 
If the armoured cable is 4mm then it could be connected to the socket (assuming the double socket is on a rfc (ring final circuit) protected by a 32A mcb, without any further protective device.
If the double socket is already a 'spur' off the rfc then you need to seek further advice on best way forward.
If only 2.5 sq mm then a protective device will be required (20A mcb!)
RCD protection by one protecting the rfc?
Not sure why there is an IP rated s/fcu in the garage at all?
[automerge]1593463134[/automerge]

'Thinking' doesn't do it. 8mm is a non standard size so doubt its that.
sq mm refers to the actual cross sectional area of the copper conductor NOT the diameter of the cable/core.
sorry i know for a precise answer i should talk precise sizes
 
It does help.
Thanks, The Sparky that fitted the cables ...etc wont answer my calls...I think maybe furloughinging or something else has affected him...I did ask what size glands were used for the hot tub cabling which is the same size cable and he said 20mm outdoor SWA Glands...does that throw light on the armoured cable size ? or not ?
 
No, 1.5 to 6 sq mm cables all use 20mm glands.

If its the last socket of 4 on a radial protected by 32A mcb. The cable supplying the sockets needs to be established as if only 2.5 sq mm there is an issue with the use of a 32A mcb in the first place
 
No, 1.5 to 6 sq mm cables all use 20mm glands.

If its the last socket of 4 on a radial protected by 32A mcb. The cable supplying the sockets needs to be established as if only 2.5 sq mm there is an issue with the use of a 32A mcb in the first place
Thanks its a 6mm armoured connected to a mcb of 32a and is the last socket...as regard to radial or ring i am unsure as the trunking runs along all 4 walls and is hard to say unless i remove all the trunking tops....It could start and end in the cu as a ring would
 
All seems a bit of a strange design, he'd have been better running the SWA back to the Garage Consumer unit and putting the bar on it's own circuit. An MCB in an Rcd protected consumer unit isn't ideal for a distrubition circuit either. If the sockets in the garage are a ring then the fused spur would need to stay, it wouldn't matter if you used 25mm cable, the entire bar area would still be a spur off the ring and the limit for that is just 1 single or double socket.
 
All seems a bit of a strange design, he'd have been better running the SWA back to the Garage Consumer unit and putting the bar on it's own circuit. An MCB in an Rcd protected consumer unit isn't ideal for a distrubition circuit either. If the sockets in the garage are a ring then the fused spur would need to stay, it wouldn't matter if you used 25mm cable, the entire bar area would still be a spur off the ring and the limit for that is just 1 single or double socket.
Hi, I am sure it has its own 32amp circuit connected to the garage cu..why it has a fused spur before going outside ??
 
Hi, I am sure it has its own 32amp circuit connected to the garage cu..why it has a fused spur before going outside ??
Your photo shows a fused spur labelled "Pauls Bar" with the SWA cable heading out of it?

Not sure why it has an IP rated enclosure either given it's right beside a socket that doesn't. Strange setup.
 
some armoured cable has its size embossed on the outside, every meter. will be something like BASEC CABLE BS123455* 3 X 4SQ MM
have a good look, it might give you a clue as to what cable it is.
 
I have taken the covers off today of the twin socket and fused spur. It seems that the twin has x2 twin and earth cables feeding it and then x2 from there feeding the fused spur with the 6mm armoured inside. This then is sent to an opened end (dead) to the bar shed.
View: https://flic.kr/p/2jhz878

View: https://flic.kr/p/2jhz84N

View: https://flic.kr/p/2jhz8iq
View: https://flic.kr/p/2jhz8jC
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
stoke
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
What type of consumer box
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
stevenson166,
Last reply from
stevenson166,
Replies
28
Views
2,699

Advert

Back
Top