Thats correct, however, the DNO own the supplying cable, fuse etc (the important bit). the meter is only to monitor usage, not to provide any fault protection.

Therefore, they have the final say on how you connect your installation to THEIR supply.

Some DNO's will not connect a new supply without seeing an install certificate from an NICEIC or ECA registered member.

You are thinking far too much about this!!!

To clarify

1) The DNO own and maintain the supply cable and cutout/fuse holder
2) The electric company who you buy your electric from own and maintain the cables from the cutout to the meter and the meter.
3) The home owner is responsible for the cables from the meter to the consumer unit. This is why some suppliers charge if you need to upgrade from 16 to 25mm tails.
4) There is no obligation for a supply company to fit a isolator, BUT almost all will fit one on new builds or on request. Some charge, some don't.
5) The DNO or the supply company have the legal right under the ESQCR to terminate your supply if they HAVE REASON TO BELIEVE that your installation does not comply with the currant regulations.
6) The DNO is responsible for determining the route, length & CSA of the meter tails. Because different DNO's have different ideas on how things should be done, it is difficult to get a conscious of opinion.

I recently went to 5 new builds with the meters outside in box's. None had isolators and the meter was 5 meters from the cu.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
whose tails and how would you like it sir?
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
15

Thread Tags

Advert

Thread statistics

Created
No.15,
Last reply from
spark-doctor,
Replies
15
Views
2,769

Advert

Back
Top