No, No, No.Her is the final video. I have a roll of audio cable, it is 0.5-1mm diameter copper which should be fine for the 3W led, but I just used both veins for safe measure.
The insulation around audio cable is not rated for 230V (or 240V as it more commonly is in the UK) even if it is the right CSA.
This is an accident waiting to happen.
You need to find the break in the original wire and replace it with proper mains cable or re-terminate it if the break is at an accessory.
Have you checked the cable in the loft? Could it have been nibbled by vermin?