I think you, ve made the right choice with the rcbo CU. I would also add that the 19ms trip time is very normal for the rcd in my experienceMany thanks for all the replies.
I've gone with the RCBO board and will report back when it's fitted ?
I think you, ve made the right choice with the rcbo CU. I would also add that the 19ms trip time is very normal for the rcd in my experienceMany thanks for all the replies.
I've gone with the RCBO board and will report back when it's fitted ?
You are quite right that any faults should be investigated before swapping stuff. But in this case the IR results are OK-ish (low, but not out of a EICR pass) and it seems other checks like clamp for leakage, etc, have already been done but nothing pointing to a definite cause.Is all well swapping a board but will not solve the problem with out being fixed.
Me find the fault before swapping.
This is one of those unusual cases.do a full test before fitting new CU...could save a LOT of headache afterwards
Lets put ourselves in the customers shoes, internment RCD tripping over a very long period of time. We dont know the full story of any intervention over this time.
Changing to RCBO's the expense of this for arguments sake £600 and the fault although narrowed down to hopefully one circuit, BUT it still tripping you are not going to be happy.
IMO drilling down on each circuit with IR testing is the way forward, and start investigating the the circuits with the lowest IR.
You are assuming that there is "a fault". An accumulation of "intentional earth leakage" is not a fault in the conventional sense. Its what happens when the design of the installation is no longer adequate for the practical needs of the installation. It's a situation that we will encounter progressively more as time goes on due to the inevitable increase of electronics in the home.IMO drilling down on each circuit with IR testing is the way forward, and start investigating the the circuits with the lowest IR.
If this was a simple case of a reported tripping fault and the first action is to suggest a board change then yes, that is going to be a big disappointment for the customer as it probably won't fix any real fault. They would have every reason not to be happy.Lets put ourselves in the customers shoes, internment RCD tripping over a very long period of time. We dont know the full story of any intervention over this time.
Changing to RCBO's the expense of this for arguments sake £600 and the fault although narrowed down to hopefully one circuit, BUT it still tripping you are not going to be happy.
They have low insulation 1.7 megohm on a global reading associated with problems, in my view this needs investigating.You are assuming that there is "a fault". An accumulation of "intentional earth leakage" is not a fault in the conventional sense. Its what happens when the design of the installation is no longer adequate for the practical needs of the installation. It's a situation that we will encounter progressively more as time goes on due to the inevitable increase of electronics in the home.
Taking a conventional approach to this particular problem is in my view not what's required.
They have low insulation 1.7 megohm on a global reading associated with problems, in my view this needs investigating.
It is suspiciously low, but I presume that @HappyHippyDad will be doing per-circuit testing as part of the board change and at that point we will find out if it is 8 circuits in the 13M region, or 7 are > 200M and one is the 1.7M lurking like a leaky toad for investigation.They have low insulation 1.7 megohm on a global reading associated with problems, in my view this needs investigating.
Tangent, but I'm glad you've pointed this out as I've heard more than one person say "I won't bother with IR tests as the RCD would trip if it's a problem!". I think a 0.02Mohm IR results in a current of about 11ma, so even lower IR needed to reach trip current of a 30ma RCD.It's not that low ,It's well above the range of tripping an rcd
There are so many reasons that is a stupid attitude!Tangent, but I'm glad you've pointed this out as I've heard more than one person say "I won't bother with IR tests as the RCD would trip if it's a problem!".
There are so many reasons that is a stupid attitude!
While the regs have values in the 0.5M to 1M region as a 'pass' that is too low for comfort unless there is a good reason to explain it, for example an old warehouse with dozens of dusty light fittings all adding up to the ~1M result.
- L-N insulation faults can start fires, not detected by RCD
- Low IR can point to future problems due to water ingress or degraded cables
- Low-ish IR can reveal 'live' metalwork that is not able to trip an RCD until someone touches it, at which point if the RCD is faulty then someone probably dies.
Hopefully we will get an update at some point with the results of testing the new board and if that really solved the problem, and if not how it was finally pinned down.
I think it's ok pal, I know the comments weren't aimed at me!I do believe you have misinterpreted Tim's post
The 1Mohm figure is being talked about in the context of an rcd trip not as a good IR value