I have just completed an EICR.
The install is TT, Ze is 308 ohms.
Zs on all circuits is <1.5 ohm due to bonding.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.

The lighting circuit had N-E IR readings of 0.27ohms. All other circuits were >2M ohms.

My question is why did the RCBO not trip instantly when I powered up this circuit through the RCBO?
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
Advertisement - Content continues below

telectrix

-
Mentor
Arms
Esteemed
N-E fault. do you mean 0.27 ohms or 0.27 M ohms? either way a N-E fault can stop a RCD from tripping.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #4
My initial post may sound a bit confusing as I'm tired!

Put simply, the IR test N-E is 0.27 ohms not M ohms and the RCBO does not trip when the circuit is powered up. It trips as it should do when tested.

Why does it not trip instantly when the circuit is energised with a N-E fault of 0.27ohms?
 

telectrix

-
Mentor
Arms
Esteemed
the N-E fault is inhibiting the RCD from tripping. the theory escapes me, but believe me, it's a fact.
 

Paignton pete

-
Arms
Esteemed
My kewteck 64 does not trip an rcd on a TT system if the Ze is too high. If it’s over 300 - 400ohms.

This has happened a couple of times.

If I put an additional rod in lowering the Ze it works fine.

Don’t know why.
 

Risteard

-
Arms
Esteemed
My kewteck 64 does not trip an rcd on a TT system if the Ze is too high. If it’s over 300 - 400ohms.

This has happened a couple of times.

If I put an additional rod in lowering the Ze it works fine.

Don’t know why.
Inhibition of excessive touch voltage.
 
The neutral return even though there is a fault to earth which sounds like a solid connection between the two may not necessarily decide to follow the earth path. It just keeps to the neutral because it is possibly the path of least resistance being a TT system hence no imbalance.
 
D

Deleted member 105166

If you clamp the lighting circuit L+N, what leakage value do you measure?
 

Des 56

-
Arms
Esteemed
Your relatively high 270 thousand ohm resistance of neutral to earth (combined with a high resistance earth return) is sufficiently high enough that there is not enough leakage to earth to imbalance the RCBO in the normal working conditions
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #11
My kewteck 64 does not trip an rcd on a TT system if the Ze is too high. If it’s over 300 - 400ohms.

This has happened a couple of times.

If I put an additional rod in lowering the Ze it works fine.

Don’t know why.
Yes, but the zs is <1.5ohms.
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #12
Your relatively high 270 thousand ohm resistance of neutral to earth (combined with a high resistance earth return) is sufficiently high enough that there is not enough leakage to earth to imbalance the RCBO in the normal working conditions
It's 0.27 ohms Des, not 0.27M
 

davesparks

-
Mentor
Arms
Esteemed
.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.
When you tested at the RCD did you disconnect the outgoing conductors or disconnect L and N of every circuit?

How does the tripping of your spare RCBO prove that this RCD is faulty? Surely all that proves is that you have a working RCBO?
Testing the RCD with all outgoing conductors disconnected proves whether or not the RCD is working.
 
uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Why isnt the RCD tripping? in the Electrical Forum area at ElectriciansForums.net

uHeat Banner - Forum Discount Available
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom