Thank you for all your answers, I didn't expect such fast responses like this, so I didn't check the forum so often. But I still have some concerns:
1. Could you explain the term "integral trip" for me, it's quite new?
A safety trip that is within the device, often not for user reset as they happen when a problem has occured and the cause needs verifying before it is replaced or reset.
2. And about the floating neutral, if all our appliances are three-phase, and we supply them with 3-phase power, will this happen???
This is more complicated to explain but in brief, the loss of a N be it a loose connection or other fault could mean the N bar's potential can climb to upto 400v in relation to any other phase - for equipment using 400 or 230v and a N this can be disasterous and can destroy equipment and its possible as a cause of fires.
A few years ago when a spate of copper thefts from substations occured they pinched what they thought was simply an earth but it was also the N (combined E/N) and this led to many connected households having thousands of pounds worth of damage due to what is known as a floating N where voltages of up to 400v appeared between L and N on a normally 230v system.
Thanks a lot for all the answers