May be the prof is going down the lines that thers willbe less amp drawn down each phase if 3 phase is used as aposed to single phase , as it is the amps that kills you not the volts , but thst would be on the dno side , i can't see how it would make the house electrics any safer

I haven't a bloody clue what you're saying here. The current drawn by the load is irrelevant when you touch a live conductor. When that happens, it's the current YOU draw as a result of your body resistance which is vital.
 
As far as DNOs are concerned, the only time a three phase supply is required in a domestic installation is when load demands it, that is when there is a load which exceeds a 100A supply (around 27 kVA). Above that, load has to be split across multiple phases. Other than that, occasionally a posh household with a need for specific multiphase equipment (swimming pool, large electric gates etc.) would obviously require such a supply. Given a 230/400V three phase, as is standard across the UK for LV supplies, it's hard to see how it could be thought of as safer.
 
it's geneerally safer as the Electrical Trainee.s would not be let loose on it.
 
So if a 3P supply had been provided in a premises way back when (Lets say a commercial one), would the supply cable have had smaller CSA's per phase than if only a single phase had been installed, meaning that it would be limited on its single phase operation (to 60A?)
 
I haven't a bloody clue what you're saying here. The current drawn by the load is irrelevant when you touch a live conductor. When that happens, it's the current YOU draw as a result of your body resistance which is vital.
Sorry i was trying to think of a reason why the prof thinks that 3 phase is safer , but of course as you say , your body is the load when you touch the line so it want make any difference with 3 phase or single , i must engage my brain in future :)
 
Sorry i was trying to think of a reason why the prof thinks that 3 phase is safer , but of course as you say , your body is the load when you touch the line so it want make any difference with 3 phase or single , i must engage my brain in future :)

No problem Flanders. I'm being a bit of a smartarse because I train people in this (for a DNO).
 
So if a 3P supply had been provided in a premises way back when (Lets say a commercial one), would the supply cable have had smaller CSA's per phase than if only a single phase had been installed, meaning that it would be limited on its single phase operation (to 60A?)

Not usually. We supply either 100A single phase or 3 x 100A three phase supplies as a matter of course, for total current metering. The standard at one time, before people had such large demands on supplies, would have been single phase 60A supplies, so I suppose 3 x 60A wouldn't have been unheard of. Anything above 3 X 100A would then necessitate ratio, or CT, metering.
 
It appears that the OP is in Vietnam, so maybe there is more to this than meets the eye.

Other countries use all sorts of voltages, like the USA where you have a choice of a few different voltage LV supplies. So maybe they have a three phase supply which is different to and of a lower Uo than their standard domestic single phase which would account for it being 'safer'.
 
It appears that the OP is in Vietnam, so maybe there is more to this than meets the eye.

Other countries use all sorts of voltages, like the USA where you have a choice of a few different voltage LV supplies. So maybe they have a three phase supply which is different to and of a lower Uo than their standard domestic single phase which would account for it being 'safer'.
Possibly. It would be nice, as always, if the OP did the courteous thing and either became involved in his own post or thanked the very experienced guys on here who have responded (I'm not including myself)
 
I'm giving him the benefit of the doubt (I can be nice occasionally) as I don't know what times one he is in etc,
 
Thank you for all your answers, I didn't expect such fast responses like this, so I didn't check the forum so often. But I still have some concerns:

1. Could you explain the term "integral trip" for me, it's quite new?

2. And about the floating neutral, if all our appliances are three-phase, and we supply them with 3-phase power, will this happen???

Thanks a lot for all the answers :-P
 
Thank you for all your answers, I didn't expect such fast responses like this, so I didn't check the forum so often. But I still have some concerns:

1. Could you explain the term "integral trip" for me, it's quite new?

A safety trip that is within the device, often not for user reset as they happen when a problem has occured and the cause needs verifying before it is replaced or reset.

2. And about the floating neutral, if all our appliances are three-phase, and we supply them with 3-phase power, will this happen???

This is more complicated to explain but in brief, the loss of a N be it a loose connection or other fault could mean the N bar's potential can climb to upto 400v in relation to any other phase - for equipment using 400 or 230v and a N this can be disasterous and can destroy equipment and its possible as a cause of fires.

A few years ago when a spate of copper thefts from substations occured they pinched what they thought was simply an earth but it was also the N (combined E/N) and this led to many connected households having thousands of pounds worth of damage due to what is known as a floating N where voltages of up to 400v appeared between L and N on a normally 230v system.


Thanks a lot for all the answers :-P

I wouldn't worry too much at your level how a floating N actually works as it can be confusing when your learning the basics but you might impress the tutor although I believe it is beyond what he is asking you for.
 
Last edited by a moderator:
I'm giving him the benefit of the doubt (I can be nice occasionally) as I don't know what times one he is in etc,

you're lucky. sometimes i don't even know what time zone i'm in or even what day it is. :17:
 
Hi everyone,

I'm taking an electrical course at the university and the professor asks us a very tough question: "Why we use single-phase for power supply while 3-phase is much safer, more efficient? What happens if we replace all the single-phase power supply by the 3-phase one?"

So, why normally household power supply must be single-phase?

All the search on Google so far doesn't satisfy me enough because it cannot give me the benefits in terms of power or technology. So, I hope that someone here can really enlight me :(.

Thank you so much.
youd have to have little 415v warning stickers on all your sockets as well and theyd get all grubby in the kitchen
 
youd have to have little 415v warning stickers on all your sockets as well and theyd get all grubby in the kitchen
why? warning stickers only required when nominal volts to earth exceeds 230V
 