G
gobster
or are they completely related. although it is the current that kills you and not the voltage, it is the voltage that dictates the current across a load. higher voltage, higher current. when we talk about safety we talk about fault conditions, not operating conditions, thus SELV and not SELANot necessarily true. If the line voltage were the same as the present phase voltage (i.e. 230/132 instead of 400/230) and single-phase loads were connected in delta, then the equipment wouldn't consume any more current but the voltage to earth would be lower, therefore safer. Of course there is a competing factor that both wires are live to the touch instead of only one (normally). As it happens, this system was used quite widely in the past, and it is still standard for shipboard supplies. The reason Germany for example adopted the un-polarised Schuko plug was that at the time, 3-phase delta was in use and both pins could be lines, so it didn't make sense to distinguish them. These days, 3-phase supplies are still in use in continental houses but star, rather than delta.
My take on it is the difficulty of handling large loads on small systems. If you have a 100A SP supply, you can run a 50A shower load, given diversity, without any specific complications. A 3-phase supply of the same total capacity would not support such a large load on any phase, so it would have to be 3-phase, which is more expensive. It is harder to utilise diversity on say three 25A main fuses than one 60A.
These two true statements are totally unrelated to each other!