N
NUGGY
Where the tails run from meter to CU/DB is not normally sealed, just a removable cover plate.
with a seal on it lol
if meter is sealed and tails need changing this is where mr henley comes in![]()
Some meters have a split terminal cover on the consumers side that is not sealed and has an isolator behind the cover so you can work dead occasionally some DNO's fit an isolator after the meter which has a split cover arrangement allowing access to the consumers side terminals only
Ok, I know that, what I was trying to say was perhaps I could assume that the distributor's requirement for the csa of the tails on the consumers side of the meter would not exceed the csa of their own tails on their side of the meter, I just didn't explain myself very well. I'm guessing that the main fuse is probably only a 60A or 80A but I haven't checked yet.
Why do I feel like I am digging myself into a hole![]()
Years ago when you got the electricity board to connect tails after a rewire they would expect you to install 16 or 25mm² tails but the tails from the cut out to the meter where usually well undersized
I rewired my house recently - in fact, truth to tell, it's still ongoing - but I fitted 25mm tails from the new 15 way main switch + RCBO'd board to my isolator.
From the isolator back to the meter, & from the meter back to the cut out, the tails are the "old coloured" 16mm. Then the bloke came to change the meter not asked for by me, but sent by DNO and I handed him a nice new pair of tails & asked him to fit them in place of the old 16mm pair.
He refused, claiming it wasn't his job, so I now have what I think is the ludicrous situation of having 16mm "old coloured" tails from the cut out as far as the isolator, & then 25mm tails from the isolator to the CU.
The mind boggles !!!!
Last few meter changes I have seen done they changed the tails on the DNO side to 25mm² in the new colours
Yeah, I think they just wanted to stop curious people from removing the lid and killing themselves, I thought that it was a bit strange, nothing to do with them really.
Years ago the old electricity boards always sealed the henley blocks