Piratepete

Just done a domestic CU change. The cutout was 100 Amps (used to supply Economy 7 storage heaters but no longer). Existing tails 16sqmm. Therefore need to change to 25sqmm as normal.
But existing tails are routed out of the top of an external flush meter box up through the (uninsulated) wall cavity into the old Wylex FB which was mounted close to the ceiling other side of wall. Couldn't shift em let alone pull new ones through!

So, I've left em, and got the supplier to reduce the cutout size to 80 Amp at no cost to the customer or myself.
Unless I'm mistaken, taking all factors into account and Ref Method C the 16sqmm cables are rated at 87 Amps. If you also assume a 25 deg ambient they are good for 89.6 Amps.

In this case, could I also have just written a note in the 'Departures from BS7671' box? From a practical point of view, the original tails were never likely to get stressed!

If I'm not mistaken, this could also be a good wheeze to avoid changing the tails, which can be a costly exercise where they come directly out of the meter and an isolation switch is needed.:angel_smile:

Pete
 
Often see 16mm tails on 100A cut out, Do a max demand calc and see if the tails can handle it
 
Often see 16mm tails on 100A cut out, Do a max demand calc and see if the tails can handle it

Isn't the maximum demand irrelevant? Surely as with any circuit, the conductors after the fuse have to be rated at or more than the fuse? I guess that once upon a time 16sqmm tails were rated at 100 Amps.:confused5:
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Why Upgrade the Tails??
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
Piratepete,
Last reply from
Piratepete,
Replies
3
Views
1,267

Advert