Simon Torr

Wiring a garage with SWA. (domestic)

Two double sockets and two way lighting
I have a split board, RCD protected on one side, taking a feed from the RCD protected side from 20a MCB, via SWA to D/B with 20a RCD and 16a MCB for sockets and 6a MCB for lighting.
The run will be under 2 meters so Voltage drop will not taken into account.

I plan to use 2 core and earth or two core and use the armouring to provide the function of the CPC and wire accordingly (banjo).
Okay so far. ?

This is my fourth year, after three years at collage, so still have a long way to go.

Now my mentor/instructor has said to use four core SWA, so I have looked in my books, learning lounge and spoken to other electricians, and at a loss with terminating the D/B s with four core SWA, or even using four core for this work.

Help is required, any information would be helpful and appreciated
 
take your SWA feed from the non-RCD side of the board, or you will have 2 RCDs in series. use a 40A,30mA RCD in the garage. ( the 40A is it's max. load, so best to be a bit overrated than close to the limit). whilst it is perfectly acceptable to use the armour as cpc, for the extra cost involved, i'd use 3 core. what is the eartrhing system, though, and are there any extraneous matallic parts in the garage?
 
I don't undetstand why he would suggest using 4 core SWA? You will be feeding a single phase board so minimun would need the 2 core SWA as you have stated. As long as you are competent with glanding SWA and earth the armour correctly you should be ok but your tests results will show this. Also I would only RCD protect at one end most likely in the garage because if something causes the RCD to trip at the CU end then you will lose all circuits on that side of the RCD.
 
Buddy, you've got 2 RCD's in play here...

I prefer to use 2core and earth, and take a solid earth - there is nothing wrong with using the SWA strands as earth providing a solid connection is made, but i never do it this way. Alot will disagree with me on here about that, either way is fine though.

The 4core is basically a spare core, should anything go wrong to an outside shed you've got the potential to easily correct it - without digging up the cable ect... Future proofing as they call it. Its un-necessary - 3core is perfectly fine. Can't see why you're assessor has advised you that way to be honest...unless you're 3phase, but your board description dismisses this idea lol.
 
Like tele has said, extraneous?? ...the 4th core could come pretty handy here. Thats maybe what you're assessor is banging on about...
 
3 core is more than adequate for the job. only problem arises if you are exporting PME and there's extraneous in the garage. then, a 10mm bonding conductor is required.
 
Thanks for all your feed-back much appreciated.

The earthing is TN-S and brick / wood built garage and domestic single phase. use drills etc

So I take the feed from the none RCD side, 20A MCB, 3 core, 2.5mm to D/B in the garage with RCD 40A and 16A MCB sockets and 6A to the lights.

many thanks
 
I will be doing the install under the direction of my mentor/instructor and he will be testing and completing the the necessary forms which will be notifiable ie new circuit.


Thank you again
 
You should be doing the testing and paper work with your mentor monitoring you.

Otherwise you will never learn lol
 
I will be doing the install under the direction of my mentor/instructor and he will be testing and completing the the necessary forms which will be notifiable ie new circuit.


Thank you again

If he was a decent mentor, he would be answering thses questions for you and looking over your shoulder whilst YOU do all the work.