I am having a play in my shed :).

It has a 12v supply fed from a solar panel

I have 3 gang light switch which switches the following

1. 4 x 7w LED MR16 downlights.
2. 1 x 12v LED striplight (12w)(the tapelight thingy that just sticks on)
3. 1 x 20W 12v floodlight

I basically want to have a 230V backup light in there in case the battery packs up. The shed has a 230V supply to it and I originally thought I would just add a new 230V light to use when needed. However, and this is my question, would a single LED driver be ok to power all the above? If so, which one would I need with regards max wattage and constant voltage/current?

Below is a drawing of what I want.. cheers :)
(ps.. the drawing should say '4' x LED MR16's)

scan.jpeg
 
The concept is fine, the issue is your LED lamps, they will either have integral drivers or need an external driver, this is fine for your 230v mains powered option but your 12v option has no drivers in line.

You need to decide what voltage rating your LED's are going to be IE you tend to get integral drivers inside 230v AC LED lamps, your typical 12v lamp will need a driver spec'd for the supply voltage as well as the lamp rating.
I will also add that LED drivers tend to have a minimum load threshold so you also need to take that into account, the higher the maximum wattage rating may mean a higher minimum threshold meaning the driver may refuse to work if say you just had 1 lamp on it through the switching options.

PS - this is as I understand it but don't have too much to do with this stuff so happy to stand corrected on the matter. Also I will add the supplies would be on the changeover switch output lines, the load would be on the common input, kind of a reverse setup to standard, you don't want to blow up your solar set-up or short out your supply, also get a 3 position to allow a central 'off ' option you can safely lock off.
 
Last edited:
I am having a play in my shed :).

It has a 12v supply fed from a solar panel

I have 3 gang light switch which switches the following

1. 4 x 7w LED MR16 downlights.
2. 1 x 12v LED striplight (12w)(the tapelight thingy that just sticks on)
3. 1 x 20W 12v floodlight

I basically want to have a 230V backup light in there in case the battery packs up. The shed has a 230V supply to it and I originally thought I would just add a new 230V light to use when needed. However, and this is my question, would a single LED driver be ok to power all the above? If so, which one would I need with regards max wattage and constant voltage/current?

Below is a drawing of what I want.. cheers :)
(ps.. the drawing should say '4' x LED MR16's)

View attachment 45307
So total load 60watts. At 12v that is 5 amps. To allow for switch on surge get a 12v 8 amp ( or more) DC power supply ( not a LED driver).
 
If all the lighting operates at 12V, i.e. it has its own resistors built in to operate from a constant voltage, then a constant 12V is what you need. But as mentioned above, LED drivers are not necessarily the best choice and may be awkward with switchable loads. A 12V regulated DC power supply would serve the purpose, in which case, yes, you can use a changeover switch to select that or the battery as source. There is no switch-on surge with LEDs themselves (only on the mains side of drivers and power supplies) so you don't specifically need to allow extra for that, but all power supplies last longer if you don't push them to their limit.

If you want lighting with the battery removed, that would be the solution. But if what you want to allow for is the battery being low due to lack of sun, surely you want to recharge it ASAP? If it is lead-acid, it will suffer from being left discharged while you happily work under your power-supply-derived 12v lighting. A regulated multi-step charger might be a more useful solution, that could be used to top up the battery and supply the lighting at the same time, without risk of damaging either. However, most chargers will not operate the lights without a battery being connected.
 
The concept is fine, the issue is your LED lamps, they will either have integral drivers or need an external driver, this is fine for your 230v mains powered option but your 12v option has no drivers in line.

You need to decide what voltage rating your LED's are going to be IE you tend to get integral drivers inside 230v AC LED lamps, your typical 12v lamp will need a driver spec'd for the supply voltage as well as the lamp rating.
I will also add that LED drivers tend to have a minimum load threshold so you also need to take that into account, the higher the maximum wattage rating may mean a higher minimum threshold meaning the driver may refuse to work if say you just had 1 lamp on it through the switching options.

PS - this is as I understand it but don't have too much to do with this stuff so happy to stand corrected on the matter. Also I will add the supplies would be on the changeover switch output lines, the load would be on the common input, kind of a reverse setup to standard, you don't want to blow up your solar set-up or short out your supply, also get a 3 position to allow a central 'off ' option you can safely lock off.
Thanks Darkwood,

Your first paragraph says I'll have problems with the 12V supply. My shed is already running on 12V with all the lights listed.

I have a solar panel connected to a charge controller which is connected to both the battery and lights. It all works fine as is connected as it should be.

The LED driver below states 'Load 0-100W' so that wouold hopefully take care of the other problem you suggested.
 

Attachments

  • led driver.pdf
    467 KB · Views: 7
If all the lighting operates at 12V, i.e. it has its own resistors built in to operate from a constant voltage, then a constant 12V is what you need. But as mentioned above, LED drivers are not necessarily the best choice and may be awkward with switchable loads. A 12V regulated DC power supply would serve the purpose, in which case, yes, you can use a changeover switch to select that or the battery as source. There is no switch-on surge with LEDs themselves (only on the mains side of drivers and power supplies) so you don't specifically need to allow extra for that, but all power supplies last longer if you don't push them to their limit.

If you want lighting with the battery removed, that would be the solution. But if what you want to allow for is the battery being low due to lack of sun, surely you want to recharge it ASAP? If it is lead-acid, it will suffer from being left discharged while you happily work under your power-supply-derived 12v lighting. A regulated multi-step charger might be a more useful solution, that could be used to top up the battery and supply the lighting at the same time, without risk of damaging either. However, most chargers will not operate the lights without a battery being connected.

Thankyou Lucien,

It looks like the DC power supply is the way forward then.

I'm not sure I get what you mean about the battery being left discharged whilst I use the 230V supply. As in my above post, the solar panel would still be charging the battery.

This whole scenario is really just to have a bit of a play. It has come about as i did not look after the last battery properly and had to change it. During the few weeks it took me to decide to change the battery I had no lights and that is problem I wish to avoid (whilst having a bit of a play as well).
 
If you go down the driver route, would recommend you go for 75W, 12V constant voltage. You could knock up a simple DC power supply, or rob one from an old appliance. There are plenty of diagrams on internet for a 12V psu using simple components, but if it was me i would just get a CV DRIVER as you can pick them up cheap as chips
 
Hi - did you intend to keep the 230V to 12V supply on at all times?
I intend to mainly use the 12V supply from the battery. The 230V supply will only be used if the battery becomes faulty, or if the charge controller kicks in when the battery voltage becomes too low and stops me from using the lights. Thats when I will use the changeover switch.
 
Could I ask why the consensus is to use a 12 DC power supply rather than an LED driver? I realise you've already explained to an extent Lucien, but MR16's always have an LED driver so why the change in this case ?
 
Last edited:
If all the lighting operates at 12V, i.e. it has its own resistors built in to operate from a constant voltage, then a constant 12V is what you need. But as mentioned above, LED drivers are not necessarily the best choice and may be awkward with switchable loads. A 12V regulated DC power supply would serve the purpose, in which case, yes, you can use a changeover switch to select that or the battery as source. There is no switch-on surge with LEDs themselves (only on the mains side of drivers and power supplies) so you don't specifically need to allow extra for that, but all power supplies last longer if you don't push them to their limit.

If you want lighting with the battery removed, that would be the solution. But if what you want to allow for is the battery being low due to lack of sun, surely you want to recharge it ASAP? If it is lead-acid, it will suffer from being left discharged while you happily work under your power-supply-derived 12v lighting. A regulated multi-step charger might be a more useful solution, that could be used to top up the battery and supply the lighting at the same time, without risk of damaging either. However, most chargers will not operate the lights without a battery being connected.
Would this be suitable Lucien? https://uk.farnell.com/xp-power/vcs...604796549:pla-300288194765&CAAGID=14406255429
If not, could you link to a more suitable power supply if possible, thanks:)
 
A constant voltage (12V) led driver is in effect a 12 V DC power supply. The one you have linked is cheap as chips and has good regulation but as you can see the packaging is not ideal is it. It needs cooling and to be put in a box, ....
 
why not leave the 12V installation as it is, and add a 230V light totally separate from the existing lighting, just to switch on as and when needed?
 
why not leave the 12V installation as it is, and add a 230V light totally separate from the existing lighting, just to switch on as and when needed?
As soon as I saw that you'd replied I thought that's what you would be writing about :D.

Where's the fun in that Tel? Would it be cheaper.... yes! Would it be easier to install..... yes! Would it be less likely to break down.... yes!

Actually, I've decided that you're right. No change over switch, no DC power supply, just a standard, cheap switch start batten that I've got left over from a job! :)

I have however just put a changeover switch in for my sockets... very exciting for a purely Domestic installer to mess around with something different. Bear in mind this is 'my' shed not a customers, hence not as neat!
Switch.jpg switch2.jpg
 
As soon as I saw that you'd replied I thought that's what you would be writing about :D.

Where's the fun in that Tel? Would it be cheaper.... yes! Would it be easier to install..... yes! Would it be less likely to break down.... yes!

Actually, I've decided that you're right. No change over switch, no DC power supply, just a standard, cheap switch start batten that I've got left over from a job! :)

I have however just put a changeover switch in for my sockets... very exciting for a purely Domestic installer to mess around with something different. Bear in mind this is 'my' shed not a customers, hence not as neat!
View attachment 45355 View attachment 45356
as the old adage goes...... K.I.S.S. ........ keep it simple ******.:D:D:D:D
 

Reply to Would it be possible to use a changeover switch in this example? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
Replies
12
Views
589
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
960
Hi, I want to put downlights in my fire surround - possibly 3 but more likely going to be 2. They are 0.4w LED lights. I have a 12v 8w LED driver...
Replies
1
Views
472
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
556
I'd like to wire a six pin DPDT rocker toggle switch to turn a low voltage LED fixture on and off. The rocker toggle switch I have is an...
Replies
1
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock