Hi people

Anyone come across the issue of periodic testing shop freezer installations with YY cable fed loosely tie wrapped, direct from the DB board to plug socket units behind each freezer in the shop area
I want to C2 the installation as non standard cable, poor mechanical support and inaccessible isolation points, but I need some comfort that there is not a reasoning for justifying this type of installation as it seems to be in all stores

Any advice anyone. ?
 
plug/socket is an acceptable form of local isolation. maybe code it C3 for the poorly installed cable.
 
Screenshot_20190603-225555_Drive.jpg

The OSG says that the use of non standard cable is "discouraged". They may as well say do what you want, we're not really that fussed:grimacing:
 
C3 for the issues you have described.
Is there any existing certs? With signatures for design,install & test?
Also are the sockets RCD protected?
 
C3 for the problems you have identified.
 
Hi - poor mechanical support probably best judged on site. If someone were likely to trip on it or if it might be readily pulled out then perhaps C2. A few clips might turn that into a C3 for the unapproved cable.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Yy cables
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Thread Tags

Tags Tags
cables

Advert

Thread statistics

Created
young4r,
Last reply from
Charlie_,
Replies
7
Views
2,306

Advert

Back
Top