True, thanks for the help all. I'll be going back next week to finish off. One more thing (i'll try not to make it sound too confusing), i'm carrying out an installation cert (see the consumer unit layout below)
Consumer unit @ origin (4way tp) > (feeding) DB 1, & DB 2 (via 2x D63a mcbs)
-DB1 feeds new circuit 1 out of 2.
DB 2 > DB 3 & 4 (via C63a mcb) *this 4x16mm swa "piggy backs" in & out of DB3's main switch before entering DB4 (perfectly acceptable I presume but not something i've seen before?)
-DB3 feeds new circuit 2 of 2.
My main question is, with the continuation sheets I currently total 12 pages, this is because the only consumer unit I havent worked on is DB4, so I was hoping not to have to record any readings at this consumer unit & to make a note in comments instead saying "DB4 not tested" but in all honesty, because the supply from DB2 ends @ DB4 (piggy backed into main switch @ DB3) this is where I should record another ZS on a seperate continuation just to segregate the 2 boards, would you agree? If DB3 fed DB4 via a circuit breaker, could I then write on the circuit details of DB3;
Circuit details for new circuit installed & then
"all other circuits not tested"?
Sorry to ramble on!