Setup:
Consumer unit fed via sub main from a 60A fused isolator switch. This is connected to the service head MET via a 2m earth connection.

How would one go about both calculating and documenting the Zs?
Would you be treating the fused isolator switch as it’s own db and therefore be documenting Zdb1 (at point of isolator switch) and Zdb2 (at consumer unit). Zdb2 would be be the reading minus Zdb1? Or would you do Zdb1 and then the R1 + R2 of the sub main?

I’m getting myself confused so if anyone would be kind enough to talk through how you’d test this setup it would be hugely appreciated?
 
So we have meter, 3m run to fused isolator, 15m run to CU
So it’s not a sub-main, it’s the consumers tails. In that case the 15m length of (hopefully) SWA is the distribution circuit in GBDamo’s post.

You can also measure the Ze at the CU the same way you would for a more traditional setup, but you need to remove everything other than the suppliers earth and the earth to the CU from the MET before you do.
 

Reply to Zs for a CU with sub main and fused isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
598
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
814

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock