Discuss Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
cliffed
Supporter
Still having a discussion @ work about this…TNCS system DB/CU is a split 30ma RCD configuration,5/5
MCB’S are 60898 what Max Zs would you put in the column for Max measurement for the MCB😎
On a TN system I would normally base it on the MCB Zs value.
Yes, you can disconnect according to regs on 1667 ohms with 30mA RCD, but on TN-C-S it ought to be pretty low and unless it is an unusual situation, anything above the usual OSG sort of tabulated values suggests a fault in the circuit implementation which needs fixing, not a planned use of the RCD.
High current sub-main, or TT earthing, are a very different kettle of fish.
Reply to Zs measurements in the Cert column in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net