What are people's thoughts on adding a parallel 4mm separate CPC to the first point in each direction? Mathematically that would probably get the Zs under the bar. Do regs allow that?
Not really possible now… not too sure on the outcome on this one… waiting for Niceic response
 
There are 3 RM in the house… this RM travels a distance from the DB before looping into the power points….in most cases being RCD protected this would not be flagged up
It looks like its about 150m long.

Are the legs routed such that you could potentially replace them with 4mm to reduce both VD and Zs to get past RFC design goals?
 
We may be able to make this circuit compliant with the minimum of fuss.

What is this circuit likely to power? Is it kitchen, utility, heaters? Or just general purpose sockets?

Also: What is the reference method for the cable?

I think you're thinking the same as me.
 
IMG_4215.jpeg

These are the Zs values I’m getting 1.00 ohms…so compliant..but not in the length suggested by OSG…
 
What is the uplift value due to the RCD? (Before and after Zs values) as that can easily cause an otherwise good circuit to appear incorrect.
Although the relatively high readings (post #11) show it to be a long circuit, as others have indicated VD being a possible issue?
 