A bit more info as requested by
@timhoward would help.
Dropping the OCPD to 25A is a "fix" only in the sense the Zs, and (probably) VD figure
allowed, become consistent with the circuit implemented. But it is not really satisfactory as such a long RFC suggests it is something like a whole house on one circuit, and so total load would be high and might make 25A trip-prone.
Is there any point where you could break the RFC and link up two more cables as legs to make two RFCs? Taking great care of course not to have them cross-linked!