Discuss Zs on ring main high in the UK Electrical Forum area at ElectriciansForums.net

A bit more info as requested by @timhoward would help.

Dropping the OCPD to 25A is a "fix" only in the sense the Zs, and (probably) VD figure allowed, become consistent with the circuit implemented. But it is not really satisfactory as such a long RFC suggests it is something like a whole house on one circuit, and so total load would be high and might make 25A trip-prone.

Is there any point where you could break the RFC and link up two more cables as legs to make two RFCs? Taking great care of course not to have them cross-linked!
There are 3 RM in the house… this RM travels a distance from the DB before looping into the power points….in most cases being RCD protected this would not be flagged up
 
What are people's thoughts on adding a parallel 4mm separate CPC to the first point in each direction? Mathematically that would probably get the Zs under the bar. Do regs allow that?
 
What are people's thoughts on adding a parallel 4mm separate CPC to the first point in each direction? Mathematically that would probably get the Zs under the bar. Do regs allow that?
Not really possible now… not too sure on the outcome on this one… waiting for Niceic response
 

Reply to Zs on ring main high in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What would be the fault with a very high Zs at all sockets on a ring main, the sockets are an average of 68.10 . The lights are.67 and the is...
Replies
7
Views
701
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
508
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock