Is there not another 32A in the board you can swap with?
 
Is there not another 32A in the board you can swap with?
No this is an older board, the circuit I’m working on was put on a 40a type c breaker presumably to stop a b32 from tripping out which is what I tried putting the circuit on. Not the type of property you really want to dig into all other electrics in. One of them jobs I’m wishing I never started!!
Thanks for reply
 
Problem is you have no idea why it was on a 40A type C. There isn't another 32A in the board, what make is it.
 
Problem is you have no idea why it was on a 40A type C. There isn't another 32A in the board, what make is it.
Wylex the other circuits are on mcb’s, I’m altering the circuit that had previously been put on a c40 rcbo with hopes to swap it to a b32, obviously I thought something would be wrong but all seems okay, insulation resistance is low but is satisfactory for age etc of install, no major loads on the circuit. Was marked up as laundry room (where I’m moving some sockets around etc but found out it also turns of power in a room on other side of property hense high continuity readings, zs would be okay for a b type breaker but to high for a c type but finding a fault in a listed house which is rather large with difficult clients is finding itself quite challenging!. Thanks for reply
 
Problem is you have no idea why it was on a 40A type C. There isn't another 32A in the board, what make is it.
I tried putting it on a b32 same make rcbo and it was tripping every now and then, client said every 10 mins but when I go back it stays on fine the whole time I’m there, rather confusing…
 
As suggested, can you split the ring onto two radials and narrow it down that way? If you can trace the ring round the house then, you could start extending the non-faulty side radial and reducing the faulty side until you have isolated it to a smaller section of the ring and go from there?
 
Random thought. Is there a smart meter nearby? Do we know of any cases of RCBOs affected?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
C40 rcbo on ring main changes to b32 causing nuisance tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26

Advert

Thread statistics

Created
JJONESY4,
Last reply from
brianmoooore,
Replies
26
Views
3,221

Advert