OP
weevilward
Reaction score
58
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
Rodents - Very unlikely. Urban property. Kept immaculate. Recently gutted and refurbed (2 hrs ago ish)
 
OP
weevilward
Reaction score
58
Have you checked for crossed over neutrals?
Or one I had some years ago where there was an unterminated cable waaaay up high for an outside light that caused intermittent rcd issues, only tripped when it reined from a certain direction caused the end of the cable to get damp. took ages to trace
Checked for crossed neutrals, it’s not that. Can’t rule out an unterminated cable somewhere but the tripping doesn’t link with rain. And that would only take out the one RCBO.
 

Intoelectrics

-
Mentor
Esteemed
Arms
Reaction score
1,051
If the circuits are completely separated as you claim, yet both trip simultaneously then there has to be a common factor that you have not inspected. If the lights do indeed dim just before the RCBO's trip then this may point to an intermittent imbalance mains issue. Have you checked the incomer and associated connections?
 
Reaction score
1
If it worked before, then it’s a new fault developed. Wrongly connected would show up straight away.

anything new been added to any of the circuits?

Smart meter? Long shot, but it’s happened before.

Individually, we might think an outside light or socket taking in water, or rodent damage… but for all 3 at same time?
What is the likelihood of rodents? Near fields?
house mice don't need fields lol
 
OP
weevilward
Reaction score
58
If the circuits are completely separated as you claim, yet both trip simultaneously then there has to be a common factor that you have not inspected. If the lights do indeed dim just before the RCBO's trip then this may point to an intermittent imbalance mains issue. Have you checked the incomer and associated connections?
I think you’re onto something there – I got the customer to ask around in the street last night, and one of his neighbours two doors down had exactly the same issue at exactly the same time, so I am thinking there is a problem with the supply in The Street. I’ve got him to raise the issue with the DNO. The only bit I have not checked is the switch fuse and sub main from my customers meter to his CU.
 

timhoward

-
Esteemed
Arms
Reaction score
7,896
All fine for a week or so.
This is possibly the biggest clue.
As well as pursuing investigating a supply issue....

I'd be thinking whether anything might be out of circuit when testing that is in circuit during the fault.
Do they have any outside lights or anything time clock controlled?
e.g. an outside light switched by a double pole switch on the ring that is also linked to a PIR fed by the lighting circuit with all neutrals joined up, or something similarly special.

I'd also take a look at the boiler wiring if it's on the downstairs sockets circuit as when combi's are fitted all sorts of delightful things are done by our friends who fit them.

Have you tested the cooker itself? A cooker with a slowly developing N-E fault touching a bonded gas pipe behind can be the source of interesting fault chasing as the thing triggering it can be anything that is earthed.

I'd also try to be thinking about whether there is anywhere that the circuits run together. I remember one very obscure fault where cables had been pulled hard and they'd cut into some metal trunking, and vibrations changed the IR from absolutely fine to practically zero.

Best of luck and do report back!
 

Reply to Two RCBOs tripping together, no cross-connection. Need help… in the Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
962
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
725
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
497
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
10K
Advertise Here

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top