Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up.

This is one of 5 LED, low total wattage light circuits connected to one 6A RCBO breaker (so the issue could be a short or a ground leak). Zero problems with the other 4 circuits.

It was a professional installation with no issues for over 6 months then suddenly a trip. Initially identified via multimeter that one module in the master (not slave) had failed. Replaced the master and reconnected the wires as before and all was ok again for a week, until turning the dimmer up triggered a pop, not just a trip.

Light fittings all checked and everything neatly wired up and properly earthed (brass/metal fittings)

I’ve since disconnected the slave and put in a basic switch just on the problem circuit.

All initially ok, then a random trip.

Today I’ve investigated why there were 2 live/feed wires at the master module in the first place, expecting one to be the feed and the other to be a feed for another circuit - so I expected another light to be off when I removed one of them. But no, all lights working ok when 1 live removed. I then expected this ‘spare’ live/feed to read 0 volts if it were the feed for another circuit but it reads 240v. I wondered if it’s powering the slave as this spare live is on a 3 core and earth cable, but again no, the slave modules are all providing normal voltage readings.

So in summary, would it seem that 2 live feeds into either basic switch or master dimmer is the cause of the trip?

Why no issues for 6 months?

If this extra live is redundant, what’s it doing there in the first place?

Helpful comments welcome, thanks
 
Hello

What was the conclusion of your problem?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Occasional tripping x one light circuit. But is a double feed the issue?
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
LogicalLarry,
Last reply from
Lou,
Replies
1
Views
1,038

Advert