BES SPARK

Hi all, we first fixed a extension a couple of weeks ago and they were going to have a 10.5 kw convection oven so we ran a 10mm cable to it... we have gone back to second fix today but they are not having that oven anymore instead they are now having a 4.6kw oven so 20A, now the guy I was working with is saying that the cable is now too big and needs replacing, I might be wrong but am I right in thinking that we can just down rate the MCP and keep the 10mm cable? or does the cable need to be smaller?
thanks guys.
 
Thanks guys thought I was right when you got another electrician saying something else you start to doubt yourself a little
 
In situations like this, always get them to justify/prove their case.
They'll soon crawl away! :-)
 
well he wanted to down grade it because this new oven was only going to pull 20A and we have10mm cable that's why I was having the argument that we can keep the cable and down rate to a 20A MCB
 