This normally means that the Ze is too high and in applying the test current on the Line earth loop the voltage on the earth will rise above 50V and present danger on the installation.
What result did you get with the two wire method?
If 0.23 then the test should not surely be aborting due to an excessive voltage rise. With my tester I generally use the three wire method for Zs testing when RCDs are present. Not sure why you would be measuring Ze with three probes.
Using three wires for testing the Ze was how I was shown. Is this not correct then?
I think its a 2 or 3 probe test depending on what MFT you have
I have a metrel and I believe it's a 3 wire test but most books or videos Iv watched it's a 2 wire test