telectrix

~
Mentor
Arms
got a call this a.m. @ 08.10. "can you come out, no electrics at all in the house".

"OK, 30 mins, what's the address?"

30 ish year old installation wylex metalclad with an added upfront RCD (tripped and won't reset).

tripped as soon a rfc1 MCB was energised.

while i got the lid off, customer unplugged all appliances.

MFT shows 2.6Meg L-E( low but not enough to trip ). so reset RCD, energised circuit. no trip.

customer then starts replugging appliances then PING.... trip. surge protected extension lead for TV, Sky box etc.

Happy days. in and out in 40 minures £40 in arse pocket, and a happy customer.

give me 10 of these each day, i'll be a happy bunny. :46:
 
I get asked to change light switches for estate agent landlords. £45 for 5 minutes and £5 for a switch. Nice £48 profit :) get lots of them


Sent from my iPhone using Tapatalk
 


I had a similar issue the other day.





My partner phones…. “The electrics have tripped in the house”ok what was you doing when it tripped? “I started using the steam mop youruncle gave us”





Now I know my uncles sockets are not RCD protected so problemsolved J
 
steam mop? ye're too soft.give 'er a bucket and scrubbing brush.
 
Best I ever had, call-out in Brecon No lights in the day room of a care home, Gets there turns the light switch on and haypresto the lights came on, Woman just looked at me and said "I didn't know there was a switch", 5 hour round trip on a Friday afternoon I was not happy.
 
We maintain submains and reyfiled boards for a council in london, well a while back their sparks went on strike and we covered them for 3 months. 2 of us every other weeks all work after 6pm. kettle,microwave,toaster all tripping rcd water leaks basically reset the rcd and tell them to through them or turn off eletrics. I remember one day it was a bank holiday and was raining i had 17 call outs x 50= Very happy me.
 
got a call this a.m. @ 08.10. "can you come out, no electrics at all in the house".

"OK, 30 mins, what's the address?"

30 ish year old installation wylex metalclad with an added upfront RCD (tripped and won't reset).

tripped as soon a rfc1 MCB was energised.

while i got the lid off, customer unplugged all appliances.

MFT shows 2.6Meg L-E( low but not enough to trip ). so reset RCD, energised circuit. no trip.

customer then starts replugging appliances then PING.... trip. surge protected extension lead for TV, Sky box etc.

Happy days. in and out in 40 minures £40 in arse pocket, and a happy customer.

give me 10 of these each day, i'll be a happy bunny. :46:


You are...the "Scouse Spider-man" :hurray:

Found a fault on an 800KVa geny,the other day,in 3 hours,suppliers technicians having been larking for 2 days...no thanks,no cheers,nothing but payment...

Called on an elderly neighbour of me folks,who had no fridge light,found a piece of leek stuck in the switch,sat with a cup of tea,basking in the glory,felt like i'd actually helped :hurray: funny old world
 
Best I ever had, call-out in Brecon No lights in the day room of a care home, Gets there turns the light switch on and haypresto the lights came on, Woman just looked at me and said "I didn't know there was a switch", 5 hour round trip on a Friday afternoon I was not happy.
I done somthing similer light not working at school , i had been there at the beginningof the holiday so" it must me my fault " then , drove 2 hours to find out that another company had been it to test the emergency lights and left the test switch of ffc :charming:
 