Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
 
Why not put a 3 gang module away from the steel splash back and feed the sockets from there
 
get him to fit castors to the machines so he can drag them out to isolate.:mad:
 
Hi Guys
Client wants 3 wall mounted under-the-unit sockets for washing m/c, dishwasher and tumble drier. There is a lightly used ring cct available above the units. He doesn't want 3 isolation switches above the units due to having a stainless steel splash back and there's no access below.

Is it acceptable to put one 32 amp isolation switch in the ring and feed a radial from the switch to the 3 sockets via 4 sqmm T&E?

It's not a solution shown on the pretty diagram at the back of the Regs, but I don't see why not?

Cheers

Pete
Yes that’s very helpful – why not reply to Piratepete post more obliging, rather than being silly!
There you go Tel consider yourself severely chastised lol
 
The 4mm shouldn't be overloaded if clipped direct, it can handle 37A, and I assume the OCPD is a 32A breaker. However, it would overload the point of the ring where this 'branch' originates from, hence why I wouldn't do it. Just extend the ring and forget about isolators!
 
@kingeri Yeh but those machines may all be rated at 3kw if they were going at the same time...maybe marginal though
 