Don't understand why you're having trouble with this?
The conductance ratio between steel and copper is about 9:1.
By the time you've found an SWA cable where the armour has a sufficient CSA to be a bonding conductor, you will require a larger bonding conductor.
95mm2 SWA has armour which has the equivalent conductance of a 10mm2 copper conductor. Unfortunately a 95mm2 SWA cable, would where PME conditions apply require a bonding conductor with the equivalent conductance of a 35mm2 copper conductor.
These cables would be used for supplies to other buildings where bonding would be required, the size of main bonding has already been decided at the DNO source. We are not discussing DNO supply cables.
In this case then, what's to stop you using a 4C 10mm SWA (even if you don't need one), and using the 4th core for the Bonding conductor?
Lol.
What does that mean?
Are you suggesting that this supply to another building would be larger than the DNO supply at source?
I think it is you that is having a problem with understanding.
If the main incomer requires 10mm2 bonding conductors, that would suggest the supply conductors are no greater than 35mm2.
Why would you then use 95mm2 SWA for a sub main?
length of run ,volt drop earth loop imp. etc
I have no idea why you keep referring to the supply conductor size, the point is can a sub main swa cable support bonding when the armour is used as the earth. This will nearly always apply to a three phase supply where the minimum size to support bonding would be 50.0. In this day and age people nearly always use three core cable utilising a core as the cpc for single phase supplies. Otherwise it would have to be 95.0 for a two core.
Because the supply conductor size, determines the size of the bonding conductor.
Yes they do nearly always use 3 core utilising a core as the CPC for single phase supplies. This is because the armour is not acceptable as a bonding conductor.
Yes exactly 95mm2 before the armour would be acceptable for 10mm2 bonding. Which nobody in their right mind would contemplate.