S
sparksburnout
Well, I'm sure the guy from WPD will be very impressed with those qualifications when he comes to put his service head back together. Let us know what he says?
I understand that I may have been hasty to take apart the service head but I have a job to do and I don't want to be wasting time. I'm not going to lose any sleep about cutting some tallies off. I'll phone up the suppliers, If they're going to get upset about it then I'll take it up with them.
Now to sound like a complete -------: while I'm new to the domestic game (and service heads!), I am an electrical engineer trained to degree level through an apprenticeship with 15 years experience in industrial electrics.
Back to the original problem: I've finally found the water bond behind a kitchen panel underneath the sink. I have absolutely no idea where it goes. Every single cable that exits the consumer unit goes up some trunking straight in to the ceiling void. There is no TT spike or cabling anywhere to be found.
Well, I'm sure the guy from WPD will be very impressed with those qualifications when he comes to put his service head back together. Let us know what he says?
Back to the original problem: I've finally found the water bond behind a kitchen panel underneath the sink. I have absolutely no idea where it goes. Every single cable that exits the consumer unit goes up some trunking straight in to the ceiling void. There is no TT spike or cabling anywhere to be found.
That may be because somebody decided to turn the TT into a DIY TNCS.There is no TT spike or cabling anywhere to be found.
That may be because somebody decided to turn the TT into a DIY TNCS.
But as above. It doesn't matter if you have a job to do. Unless you really know what you are doing, (and with respect, you have demonstrated that you don't) what you have done is dangerous. There's nothing between the base of that old, shaky looking service head and the substation, maybe a 600A fuse there. Instant meltdown and ambulance if you get it wrong.
What continuity reading do you get between the water bond cable in the kitchen and the consumer unit earth bar?
Daz
What have your Ze tests shown (with any bonding removed)?
), varies by different DNO. Mine SSEN, allow electricians in government approved schemes, to remove seals where necessary, remove main fuse, to carry out work on customers tails. Replace main fuse, put on SSEN temporary seal and ring them with details. Check with your DNO to find their policy on seal removal.This is the whole problem.
IF the supply is TNCS then technically I can't do the test without taking the service head apart and people get really shitty about that, apparently.