Just double checking calcs if anyone bored!

So for a block of 3 flats with no gas services- all flats same. +communal stairs over 2 floors (LED light few small panel heaters)

Flat:
Kitchen Ring (32a) (32)
Ring (32a) (12.8)
Oven (20a) (13)
Hob (32a) (16.6)
Immersion (16a) (16)
Lights1 (6a) (3.9)
Lights2 (6a) (3.9)
Heating1 (20a) (2x Dimplex Monterey Panel Heater - 2000w) (15)
(Heating2 (20a)(2x Dimplex Monterey Panel Heater - 2000w) (15)
(heating3 (20a) ((2x Dimplex Monterey Panel Heater/towel rail - 1000w) (15)

Do I stick with 32+32+20+32+16+6+6+20+20+20 x0.4= 81.6amps

Advise a TPN 100a supply is needed- and stick a 4way Ryefield in with 3x 100a fuses (flats)+ 1x 60a (L/L)

OR
32+12.8+13+16.6+16+3.9+3.9+13.7+13.7+13.7=139.3!!!!!

my heads telling x 0.4 would be fine- but I know thats just the quick/lazy method
appreciate any advise
 
I get 101a per flat. That is
32a x 2 = 64
4x 20 = 80
2 x 6 = 12
+ 16
= 172x 40 % = 68.8 + 32 = 101a
But in reality would shave those figures down by applying diversity to cookers/heaters and so on. I would agree Ryefield 100a 3p+n dunno what the 60a is for?
 
Last edited by a moderator:
So onsite guide pg. 118 you see highest load plus 40% of remaining load. Hence 32a at the end there are three I only factored in 2.
 
Hi - I used the OSG, busted 110A and started drinking. Doesn't seem right, does it ? (I mean the current draw)
 