Morning guys,
I'm just after a bit of advice. I carried out an EICR on a commercial premises yesterday (no periodic since 1995). 3 phase out of the meter into Henley blocks then split between 3 distribution boards. Two single phase (one old 7 way rewireable wylex board and one single way proteus board) and one enclosure housing only a 3 phase mcb feeding an oven.
What is best practice to record in the main switch/circuit breaker on the EICR? They obviously don't share anything common apart from the 1361 cutout fuses. Any help would be appreciated!

IMG_5544.JPG
 
Well have you removed the covers for inspection purposes? if the don't have covers at all I would be more concerned with that issue, than what main switch I should be quoting in my EICR.
oh sorry, yes, the covers have been removed for the inspection, it wasn't found like that!
 
Looks a right lash up the conductors between the Hager mcb and the trunking are not suitably enclosed.
 
Looks a right lash up the conductors between the Hager mcb and the trunking are not suitably enclosed.
Yeah it's a bit of a mess, there were a lot of faults on the general standard of wiring and IP ratings. With no single point of isolation would this go in as C3?
 
If I were doing the EICR for an insurance company, who have less than intelligent conditions of addressing all C3s, then it would be no code as the switches are all in close proximity, if it were being done privately then C3 on the schedule of inspections as this would be a recommended improvement for safety. N/A on the installation details and each individual main switch identified in the schedule of test results.
 
If I were doing the EICR for an insurance company, who have less than intelligent conditions of addressing all C3s, then it would be no code as the switches are all in close proximity, if it were being done privately then C3 on the schedule of inspections as this would be a recommended improvement for safety. N/A on the installation details and each individual main switch identified in the schedule of test results.
I don't really get that what difference does it make. Whether someone ignores the C3 is not a reason for not including it.
 
I don't really get that what difference does it make. Whether someone ignores the C3 is not a reason for not including it.
If there is a minor recommendation for safety that will cost a customer significant sums to address for minimal gain I feel this is counter productive and not a professional approach. Having someone aware of an issue that could be addressed at a time something else is being changed is good, forcing someone to immediately and without fail to install a single main switch for close grouped boards is not good.
 