J

James has

Hello just wondering if this is correct its all working fine just want to double check


DSC_0718.JPG
 
No. You will have basic insulation visible outside of the enclosure. You should be clamping the sheath. You should be measuring and recording the Zs and rcd trip times in order to confirm compliance (safety).
 
ok i will correct that but are they in the right order ?

That's difficult to tell from here. The connection unit appears to be marked right to left, L, E, N. It appears you may have the connections incorrect, without being able to see the colour markings of the 'supply cable', which appears to be recent colours?

I would recommend you employ an electrician.
 
Don't know about anyone else, but I can't see two conductors in the earth connection.
 
Don't bite folks! It's a wind up.
 
I would probably agree, the picture is a bit like a how not to do it picture.
Cables in wrong locations, badly terminated, wrongly clamped, poorly stripped, but at least the earth is sleeved!
 