Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here
 
Ditch your multi function tester and get yourself a proper dedicated insulation resistance tester:)
I prefer that its me who decides when a test can proceed, not some all singing and dancing modern playtool that is all things to all situations
 
Ditch your multi function tester and get yourself a proper dedicated insulation resistance tester:)
I prefer that its me who decides when a test can proceed, not some all singing and dancing modern playtool that is all things to all situations
Just ditched my Fluke and bought a shiny new Megger 1731 on NIC assessors advice ! So would it be likely a stand alone IR tester would do something? As I ditched my seperates for the Fluke !
 
Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here

Sounds like fun.

How many separate circuits are you talking about?
 
Tried again today, still at job now searching for any issues ! 32 Meg L-N & L-E but N-E won't test nor will L+N -E with switches closed, open, ufh Rcd spur found and isolated, lamps out & in, dimmers swapped for standard switches, main switch off at cu and only L&N out N bar /
mcb ! Anyone seen this before ? Fault somewhere ? I'm cracking up here

So, just break the circuit into sections and home in on the fault.
 
So, just break the circuit into sections and home in on the fault.
Love to but some of the fault is on a few circuits as whole board / global IR test was sitting at >999Meg until around 5 seperate circuits were brought online via breakers and then any one of them caused bonkers readings !!
 
DO NOT fault find using global IR ............ it won't work ( well it might eventually) but its not the way to approach this...

You need patience, a note book and a pen ............. then test each circuit (cpc's connected to CU) one by one then it will be easy............................ and if you find yourself going round in circles, then walk away and go back afresh another day.
 
Worse thing you ever did was to ditch your perfectly good separates for some temperamental mft, I won't give one van space. What does it do when you try to test N/E.
 
Worse thing you ever did was to ditch your perfectly good separates for some temperamental mft, I won't give one van space. What does it do when you try to test N/E.
Goes to ramp up the volts but stops mostly max 15V and reverses back down again, locks out, whereas L-N L-E ramps straight to 550V approx
 
Have you read the instructions to see what this indicates.
 
To be fair I wanted one since company I worked for had 1553 years ago and it was fantastic and this one is a work of art and technologically another universe but this blinking job is driving me bonkers cause it won't let me get a reading L&N to earth or N-E as is refusing to allow 500V or even 100 V test ! Can't see any reason why
 