J.C.E
afternoon guys
think i know answer to my question but wanted to double check
my barber (quite friendly with him so wanted to help him out!) asked me to do his barber shop eicr (only a small 6way c/u) anyways just had a brief look and its an old board with wylex push in reto 60898s- no rcd protection
the shop is ground level
would you guys c2 no rcd protection to socket outlets or with commerical is it different?
head says it just same as it would be for domestic so c2
If a non rcd protected socket was right by an external door and likely to be used for outdoor equipment C2, otherwise C3 for the ground floor sockets. (Providing acceptable EFLI readings obtained)
Are they likely to be using Portable /mobile equipment outside?
Do any unprotected sockets give rise to danger?(external influences)
This would influence my choice of code
Tis not the socket which gives rise to danger but appliances using said sockets. Don't worry about the ifs and maybes the fact is they have no rcd protection and this is the statement of fact you use, Code it, move on.
or with out extension leads out side .
I'd bring it up to current regs and put a split load board in, the equipment being used is all handheld used day in day out by an unskilled person and members of the public will be in the premises. What's the point in having regs if no one is willing to bring old installs up to current regulations? Otherwise they'll be installs 20, 30, 40 years old that aren't to current regs but loads of C3's which never get done!
it is down to the test engineer what he thinks at the time .
I agree, can't really give a definitive answer without personally being at the installation.
However (in line with numerous electrical bodies) also can't generalise socket outlet's no rcd protection as C2. And in doing so declare thousands of older domestic and non-domestic installations as unsatisfactory.
.......................... How old is the installation?
That said a barbers shop, with plug in accessories and water ................. RCD would be a good idea............
If there are no stocks in freezers -to spoil ,
or things than despiratly need recharging overnight .
Pushing for RCD sounds more than sensible
(if a fault develops at night , shop is more likely to still be there - electrics full of hair)
(It's the reason regs tighten --Improve )
Do the insurers think there should be RCD protection? And do the manufacturers of the shavers say the equipment is recommended to be used with an RCD? Just wondering. But I would go with C3 as there would no doubt be a significant improvement to safety for the barber and customers. Maybe RCD sockets?
I can't really see there is a likely danger taking into account the history i.e. how many people have been harmed for lack of an RCD? Probably none. Given the caveat of post no. 4
The clippers and hairdryers get a huge amount of wear and tear on the flex near the appliances with all the constant moving about. This puts the risk of shock at a higher level than most portable appliances. Just something to bear in mind generally.
C3 with a tin hat for me Mr. Wilkes.
J.C.E - I'd explain the value of upgrading the board to your mate the barber, a dual RCD unit wouldn't break the bank, but if finances are tight and the circuits test out ok an upfront RCD would be a definite improvement pre EICR, and of course said RCD could have been there for quite some time... This could avoid a close shave in the future.:D
Yep that's about the short back and sides of it ........:)
This is where the regs need to be more difinative, everyone has different opinions of what coding to give and should a board be upgraded, personally myself I recommend upgrading to a split load or RCBO board due to the fact that most cables are less than 50mm depth and there's more and more technology being plugged in and used, more garden equipment like lawn mowers and strimmer etc. Plus it brings it up to current regs, sooner or later installs need to be brought up to current regs otherwise they never will.
I appreciate that using equipment outdoors is a significant factor for specifying RCDs or coding an installation that lacks them. But being pragmatic for a moment, hairdressers use electrical appliances constantly, handheld sometimes with damp hands, pressing the exposed metal parts against their customers' bare skin and often rubbing against the flexes. They are then stood inches away from running and splashing water and often amongst cutting tools. Some of the appliances may be grey imports, I have often seen them used with unapproved adaptors. The hedge trimmer and lawnmower are probably still more worthy of RCD protection, but hairdressing must rank fairly close. Whether that has any impact on the boundary between C3 and C2 is another matter.
What's the difference between a barbers and a hairdressers.... Does this place have any instantaneous water heaters? Even if it doesn't and it's an old school barbers with copies of razzle and sawdust on the floor I would be tempted to C2 it. More info required in my view; grey imports and wear to flex etc have been mentioned, but at the end of the day you use your experience and discretion. I appreciate it may be a tip top pme (or other) install with superb Zs's, but without more info it's hard to code it accurately. I don't think in this instance, if applicable, the issue of outdoor equipment is that relevant. I would be far more concerned with the constant activity within the barbers itself.
J.C.E
Earth
rcd protection- barber shop
J.C.E,
NDG Elecs,