Here's a Crabtree double socket I had to replace FOC for a customer. Switches no longer able to be pressed into "on" position, and no power output on either half of socket. Been installed just over a year, had a reasonably high load: washing m/c plus tumble dryer, both running off one side of the double socket via a short 13A extension lead (as the double socket was too far away from the washine m/c and dryer). Terminations all good and tight, no sign of any thermal damage around terminals. Note the slight bulge near the left hand (as you look at the photo) earth terminal. Took it apart: plastic around switch springs had melted, meaning contacts no longer able to move.
Yeah, I'll be running my Crabtree stock down, I reckon.