You have the wording there in the text to guide you on what is needed.
So you need to have a circuit diagram fully labelled from transformer to charging unit 400V only including at least block diagrams of distribution boards, metering or consumer control equipment and showing the total earth fault path for the charger.
As part of the electrical contract, the client is considering an electric vehicle charging unit in the car park supplied from the existing TNC-s supply in the main hotel building. ….
Draw a fully labelled circuit diagram illustrating the three phase 400V supply system and earthing arrangement from the substation transformer through to the charging unit. The diagram should show the total earth fault loop path for the charging unit.
Your diagram does not need to show the complete detail of distribution boards, metering or consumer control equipment although the diagram should, as a minimum, indicate a connection point for each item of equipment.
Your diagram identifies units along the route but has no indication of line(s), neutral, earth, does not show the separation of the TNCS earth or the earth fault path.
You have shown the supply earth and the line conductors.
Use of colour may help to identify items and more comprehensive labelling would also help.