The earthing system has not been stated. If it's TNCS then testing to a local socket or other earth is not sufficient to verify compliance. If the service requires bonding then it will have to be in 10mm minimum which can only be verified by a combination of testing and visual inspection.
Although this test would prove if the water service was not extraneous and therefore not need bonding.
 
I am hoping all this kick-board nailing,has not covered up the stop-cock? This would or should,with a little prying,tell you what type of pipe arrived-and left,the cock. Giggerty.
 
Although this test would prove if the water service was not extraneous and therefore not need bonding.

As others have said, there would be other possible parallel paths. My scheme technical guidance to test to see if a service is extraneous; would be to isolate the supply, remove EC and test between supply earth (or MET) and pipework concerned.

As an aside, with incoming plastic service and predominate internal metal (e.g. water), a test could be carried out to verify if the internal service was extraneous or not. Majority of such installations I've see, have the service bonded after the plastic. Why for so?
  1. This could be that the test confirmed the pipework required bonding
  2. Installer bonded, 'cos that what they have always done
  3. Installer bonded, 'cos at some point, with building alterations (new plumbing), the pipe work could subsequently become extraneous, it would not be therefore bonded subsequently (i.e. by plumber)
  4. If 3. happens, how do you get cable from one side of building to other, so safe bet to bond it in the first place
Is my thinking flawed?
 
A bit controversial, but all these questions about bonding, earthing seems t be coming from the Domestic side of our industry.
Does this not say something about the training given to newcomers to electrical installations, or am I over thinking the problem?
 
A bit controversial, but all these questions about bonding, earthing seems t be coming from the Domestic side of our industry.
Does this not say something about the training given to newcomers to electrical installations, or am I over thinking the problem?

To be fair Pete, most domestic installers haven't the reference to refer back to within the organisation, they sometimes work alone. If I have a technical question, I ask my scheme technical. Some people come here.

Its good to talk. :)
 