Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
No nor me, can't sleep very well as it is, That's me done said my piece I believe I am right, good night all.
 
Or try reading part 5 of bs 7671 and Gn8 as it’s written in black and white how to verify that pipework has a low enough resistance to ascertain the effectiveness of the supplementary bonding
 
Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
MV5BMTQ2MjMzOTczOF5BMl5BanBnXkFtZTcwMTU0MTgwNA@@._V1_.jpg
 
reg 415.2.2

"where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition:

R less than/equal to 50 V/Ia in a.c systems

Or in the case of an rcd
50v / I delta N
 
reg 415.2.2

"where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition:

R less than/equal to 50 V/Ia in a.c systems

Or in the case of an rcd
50v / I delta N

So towel rad pipe at 0.04ohms, doesn't require local supplementary bonding?
 