No the video is explaining how to test pipework to see if they require any supplementary bonding, there are other tests to ascertain that main bonding is up to scratch.
Pete check out one of your other favourites by John Ward.
No the video is explaining how to test pipework to see if they require any supplementary bonding, there are other tests to ascertain that main bonding is up to scratch.
No nor me, can't sleep very well as it is, That's me done said my piece I believe I am right, good night all.Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
That is not what bs 7671 says on the matter.
It’s the protective device for that particular location
But the test or concern is between exposed conductive parts & extraneous conductive parts in that location?
Hurry up, I've got to go to bed soon, and I don't want to be thinking about this all night!
No nor me, can't sleep very well as it is, That's me done said my piece I believe I am right, good night all.
reg 415.2.2
"where doubt exists regarding the effectiveness of supplementary equipotential bonding, it shall be confirmed that the resistance R between simulataneously accessible exposed-conductive-parts and extraneous-conductive-parts fufils the following condition:
R less than/equal to 50 V/Ia in a.c systems
Or in the case of an rcd
50v / I delta N
Have you taken parallel paths into account?So towel rad pipe at 0.04ohms, doesn't require local supplementary bonding?
Have you taken parallel paths into account?

is that working in the shires with bilbo Baggins thenGonna give it up soon, go work down the garden center, moving green stuff about, and advising Mrs Miggins on what to put in her borders![]()
what's the betting he will put them in quick and easy .What do ya think? Could always get the plumber to use push fit.
Then happy daysOf course I have, consider it and ruled it out![]()