not had one yet but I'm thinking 100 mA RCD in place of the 100a dp switch
Wouldn't be a good idea with them control gear RCBO's due to not being double pole or SPSN. The new wylex compact RCBO's are SPSN I believe.
 
Wouldn't be a good idea with them control gear RCBO's due to not being double pole or SPSN. The new wylex compact RCBO's are SPSN I believe.
Does that matter if they are only being used for circuit protection and not isolation with the main double-pole rcd supporting them.
 
Does that matter if they are only being used for circuit protection and not isolation with the main double-pole rcd supporting them.
well yeah unless you want the whole board tripping in the event of a neutral-earth fault...RCBO trips, as it's solid neutral the neutral isnt disconnected so takes out the upfront time delayed RCD.
 