When doing mock exams 17th edition the questions that always have me stumped are about general characteristics, I had a question with maximum demand and max current in choices, both seemed feasible answers
Maximum demand is generally the figure you obtain after diversity is applied to the maximum current. For example if you have three 32A ring final circuits their maximum current demand could theoretically be 96A but in reality this is not likely to happen so you apply diversity to come up with a maximum demand figure.
Right so what they are looking for is a design figure not an absolute, but in characteristic of design max current would be a consideration to arrive at max demand
Heres another strange one
7 o/c 4 - Which of the following items does not offer ‘basic’ protection:
a a circuit protective conductor.
b a socket outlet.
c a lampholder.
d equipotential bonding conductors
Yes a few of those are nothing to do with basic protection, the lampholder is the obvious one, but other answers would be correct a. And d . are for automatic
It is posing the question to see if you understand the meaning. Reg 416 will help you.
If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault
Have a look at Reg 442.2.2 mate
25) If a fault occurs in the HV system and a magnitude of fault voltage of 430v occurs between exposed conductive parts and earth on the LV installation, what is the maximum tolerable duration of the fault
a) 10ms
b) 100ms
c) 200ms
d) 300ms
I don't know how to answer this one
What needs to happen generally under fault conditions, disconnection (ADS). You are looking for disconnection times.
Lincolnshire
General characteristics
Tags Tags
general
rich3009,
rich3009,