Click Flow connectors.
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
And how would it be connected to the Earthing arrangement if there is more than one luminaire?
 
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
 
Over sleeve it, bend back and tape to the sheath.

This way the CPC is there should anyone need in the future.

Some things can be overthought if allowed to.
obviously wago'd into the other cpc where ther are 2 cables?????
 
Click Flow connectors.

And how would it be connected to the Earthing arrangement if there is more than one luminaire?
Doesn't look like there is enough room in those fittings for loop in/out and switch so assuming that is done in a JB.

Otherwise you're right, the CPC needs continuing.
 
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
If we have the same situation in mind then yes.

That is single feed to a single luminaire, all other cables terminated elsewhere; click distribution box, lighting JB or similar.
 
Are you being serious, leave it unenclosed and taped to the sheath. There is a difference between over thought and no thought.
Not wanting to start WW3 but, what requirement is there to enclose a CPC?

526.5-8 specifically refers to live conductors.

Am I missing something?
 
Interesting stuff, especially since i'm doing the 18th tomorrow.

The 4mm, if mechanically unprotected, rule is for "Protective conductors" the definition of protective conductors on P33 (BYB) does not mention CPCs but rather:-

"A conductor used for some measures of protection against electric shock and intended for connecting together any of the following:-
(i) Exposed conductive parts.
(ii)Extraneous conductive parts.
(iii)the main earthing terminal.
(iv)Earth electrode(S).
(v) The earthed point of the source, or an artificial neutral."

None of the above mentions or hints at CPCs.......

.....Except metal (none class II) accessories, which then makes the CPC a "protective conductor".


I think...
 