hi guys

I’m preparing to carry out a rewire myself on a home I have just moved into. It’s a 1930s semi. And looks like it has had a rewire in the past (black and red colours - pvc cable) Id say I’m competent to carry out the work as I am a qualified industrial maintenance electrician however I don’t have relevant domestic quals. I’ve done a lot of reading on regs etc and noticed socket heights and switches need to be of a certain height from the ground. Currently the sockets in the house sit just above the skirting board. As I am carrying out the re wire do the heights need to be adjusted to the new regs or can they be kept the heights they currently are? I will be getting the work tested afterwards and don’t want it to be picked up on after work has already been carried out

Thanks
 
the specified heights apply only to new build to allow for use by disabled persons with limited reach. .you can fit the sockets and switches wherever you want on a rewire. ( bearing in mind that they should be easy to use for you and your family ). the most usual cock-up is Consumer Units fitted in silly places. Personally, I'd not for sockets below 12" from floor level. when you get to my age, you'll see why ( back aching bending).
 
New installation, addition or alterations must be to current standard. Your rewire constitutes a new installation. Good on you for using the Regs.
to current BS7671. this does not insist on minimun heights, that's a building reg. and as i said in post#2, applies only to new builds.
 
Existing properties can be at what ever height you want ..... but in bedrooms I tend to suggest higher than "existing" to make them easier to use ...
 
How do you differtiate between new properties and new installations? Where your EICR asks the age of the installation do you put Victorian, Tudor, Edwardian etc or, say, 25 years meaning the age of the electrical installation not the age of the property.

So a complete rewire is logically a NEW ELECTRICAL INSTALLATION is it not?
 
A rewire would be an alteration to an existing installation as the supply is already there and has been in use.

I would only call an installation new when a new supply has been installed by the DNO and you're starting from scratch.

as in:

 
I'm not picking a fight, just trying to make sense of it. Would you describe it as a new installation, addition or alteration? It will need an EIC on completion, which would need stated departures, limitations and possibly risk assessments if complete compliance is not met.

That is my thinking and I welcome clarification if I am wrong.
 